#81761 - 09/17/02 10:35 AM artical 500 Help I`m buried in the code
AMP_TRAP Offline
Junior Member
Registered: 08/05/02
Posts: 3
Loc: RAEFORD
Well I`m working at a Industrial site seems the autitors had some concerns with the paint shop Code articals.well I need help.The paint building has 2 rooms one spray area and a paint storage area thet are interconected by a wooden slide door and inside the storage area the panel is plain indoor type and floresant lights plain indoor type all rec are open.Could some of you lead me in right direction with some code references maybe.They do keep the door shut when spraying but fumes can pass in there.I feel like all explosion proof would be the thing but not really up on the articals.I work here to as Electrical Maint. With your help maybe we be safe.
Top
2017 / 2014 NEC & Related Books and Study Guides
#81762 - 09/17/02 10:59 AM Re: artical 500 Help I`m buried in the code
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
If the paint room is Class1 Div.1, the room immediately adjacent is usually Class 1 Div. 2. See 500.5(B)(2).
Classifying an area is usually an engineering responsiblity.
Top
#81763 - 09/17/02 11:09 AM Re: artical 500 Help I`m buried in the code
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Article 516 covers paint booths. Specifically check 516-2. Check 516-3 (c) for the lighting question. It does not sound to me as if you are in complicance, but the code should serve as a fair guide.
Top
#81764 - 09/18/02 04:30 AM Re: artical 500 Help I`m buried in the code
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
George,

Did you mean 516.3 (D)?
I'm guessing AMP_TRAP has a Div. 2 location on his hands.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals