The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#81737 - 09/15/02 09:07 PM Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
If you are feeding a subpanel(50-125 amp) from a main service panel(200 amp) , do you need to have 4 wires to the sub panel? The grounding and grounded conductors are terminated at same place (theoretically) in the sub panel. therefore you would need to use the supplied "bonding" screw (green).right?
Please clear this up for me, as I have heard /seen many different methods on this. I have installed may subpanels with 3 wires and I REALLY want to know if I am doing this wrong.
_________________________
I did not get as think so badly as you shocked I did.

Top
2014 / 2011 NEC & Related Books and Study Guides
#81738 - 09/15/02 09:38 PM Re: Subpanel grounding/grounded
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
If you are feeding a subpanel(50-125 amp) from a main service panel(200 amp) , do you need to have 4 wires to the sub panel?

Yes

The grounding and grounded conductors are terminated at same place (theoretically) in the sub panel...

No. They are in the disconnect or main load center, whichever is first in line from the meterbase.

therefore you would need to use the supplied "bonding" screw (green).right?

No, not it the sub-panel, but in the first panel in line from the meterbase.

Note: You will need to aquire an equipment ground bus bar for your sub-panel.

Also note: You also must size the sub-feeder conductors according to Table 310.16, for 310.15(B)(6) is for "...conductors that serve as the main power feeder to a dwelling..."

[This message has been edited by sparky66wv (edited 09-16-2002).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#81739 - 09/15/02 10:02 PM Re: Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
so in the SP , you would need a ground bar? and it must not be elctrically continuous to the neutral bar?
_________________________
I did not get as think so badly as you shocked I did.

Top
#81740 - 09/15/02 10:08 PM Re: Subpanel grounding/grounded
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
It definitely is not bonded in any way to the neutral bar (except via the EGC subfeeder back to the main disco or panel, then through the bond to the grounded conductor then back to the sub panel).

No bond screw or bonding jumper in the sub-panel at all. To do otherwise would create a parallel path for the neutral current.
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#81741 - 09/15/02 10:18 PM Re: Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
ok , Thank you for the plain english. So, it is continuous , but at the main panel? ground/neutral bar at sub are seperate, but bonded at main?
_________________________
I did not get as think so badly as you shocked I did.

Top
#81742 - 09/15/02 11:01 PM Re: Subpanel grounding/grounded
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
Yep, you got it!

_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#81743 - 09/15/02 11:13 PM Re: Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
Thank You very much you may be able to help a little situation I have here on this post http://electrical-contractor.net/ubb/Forum7/HTML/000185.html
_________________________
I did not get as think so badly as you shocked I did.

Top
#81744 - 09/16/02 04:19 AM Re: Subpanel grounding/grounded
danger Offline
Junior Member

Registered: 08/01/02
Posts: 4
Loc: canisteo, ny, usa
definately a neutral problem, i've seen this scenario many times.

Top
#81745 - 09/16/02 07:33 AM Re: Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
A neutral from main to sub? or in the building? Im going out there right now.
_________________________
I did not get as think so badly as you shocked I did.

Top
#81746 - 09/16/02 01:47 PM Re: Subpanel grounding/grounded
Sean WB Offline
Member

Registered: 09/15/02
Posts: 113
Loc: South TX
turns out they kernied the neutral at service drop for the barn.there are three weather heads on the pole and it looks like a birds nest up there.I continued to have same problems today, so I am going to run a new underground service tomorrow for the barn and discontinue the overhead service.
Its either an insulation breakdown in the ungrounded conductors feeding the barn (which are 30+ years old) or I have lost a neutral at the bird nest.
Either way, this was definitely a learning experience.
I need to invest in a megger, whats a good name to get ??
_________________________
I did not get as think so badly as you shocked I did.