ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#81734 - 09/15/02 05:22 AM Non restricted breakers
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
Why are non restriceive twin breakers made if you can't use them to over fill a panel box. The only panels that can exept twins have the notch in them. What the dilio???
Top
2017 / 2014 NEC & Related Books and Study Guides
#81735 - 09/15/02 08:33 AM Re: Non restricted breakers
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Older load centers did not have notched stabs but many were approved for use with twin breakers in the positions shown on the wiring diagram. The problem was people were installing these breakers in any position and in panels that were not approved for twin breakers so they had to come up with a CTL design. They still make the breakers for use in older panels without the notches but usually cost quite a bit more.

Curt
_________________________
Curt Swartz
Top
#81736 - 09/15/02 10:46 AM Re: Non restricted breakers
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
That is one of my pet peeves. When I go on an inspection and I see twin breakers, I have to look at the wiring diagram and/or the panel model number. Some panels like the ITE (Siemans) 20-20 panel means that it can handle 20 full size breakers only. No twins. Then the contractor usually argues with me that panels can haold up to 42 circuits. Well that is true, however the manufacture of a certain panel only wants a certain number of breakers in that panel. I wish that the manufactures all had seperate configurations for their own equipment and not let everyone elses in there. It might be so much easier.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals