The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#81731 - 09/13/02 06:24 PM support of a nipple
Eandrew Offline
Member

Registered: 05/24/02
Posts: 69
Loc: seattle, wa, usa
Does a nipple need not be supported if it is equal to or less than 18 inches long? Any code references for this?

Top
2014 / 2011 NEC & Related Books and Study Guides
#81732 - 09/14/02 06:46 AM Re: support of a nipple
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I could be wrong, but I would see no need for support for any conduit less than 3' long...

No code references... Sorry...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#81733 - 09/14/02 08:04 AM Re: support of a nipple
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Sparky,
What about 344.30?
 Quote:
(A) Securely Fastened. RMC shall be securely fastened within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other conduit termination. Fastening shall be permitted to be increased to a distance of 1.5 m (5 ft) where structural members do not readily permit fastening within 900 mm (3 ft). Where approved, conduit shall not be required to be securely fastened within 900 mm (3 ft) of the service head for above-the-roof termination of a mast.

This same wording is used in the other raceway Articles. I know that nipples are commonly installed without support, but I don't find any exceptions in the NEC to premit that practice.
Don
_________________________
Don(resqcapt19)

Top