#81715 - 09/13/02 05:25 PM 210.23(A)(2)
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A new home with 3 garage door openers(5 amps each)and 3 keyless lampholders wired to a single 20 amp circuit is a violation.
Correct?
Top
2017 / 2014 NEC & Related Books and Study Guides
#81716 - 09/13/02 07:47 PM Re: 210.23(A)(2)
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
A garage door opener wouldn't be considered continuous load, so you could load a 20 amp breaker to 20 amps of non-continuous load. What is a keyless lampholder?
_________________________
Ron
Top
#81717 - 09/13/02 08:04 PM Re: 210.23(A)(2)
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA


Keyless Lampholder, with a suicide tail!
_________________________
Joe Tedesco, NEC Consultant
Top
#81718 - 09/14/02 04:23 AM Re: 210.23(A)(2)
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Ron,

I don't believe continuous or intermittent enters into the consideration of 210.23(A)(2).
Top
#81719 - 09/14/02 04:56 AM Re: 210.23(A)(2)
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Redsy,
Sorry I didn't look at the article number you referenced before dribbling at the keys. Seems you have a valid concern.
_________________________
Ron
Top
#81720 - 09/14/02 07:52 AM Re: 210.23(A)(2)
arseegee Offline
Member
Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
What is your maximum wattage listed on the keyless fixtures?
Top
#81721 - 09/14/02 08:36 AM Re: 210.23(A)(2)
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Probably 100? I have seen 200 watt bulbs used in a lampholderthough!

See this UL site when questions concerning a product arise.

http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/textsrch.html
_________________________
Joe Tedesco, NEC Consultant
Top
#81722 - 09/14/02 11:04 AM Re: 210.23(A)(2)
arseegee Offline
Member
Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Joe, the keyless fixtures we use are rated at 660W-250V. OUCH! We usually bulb them out at 100W.
Top
#81723 - 09/14/02 05:01 PM Re: 210.23(A)(2)
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
Quote:
(11) Other Outlets. Other outlets not covered in 220.3(B)(1) through (10) shall be computed based on 180 volt-amperes per outlet.


x3= 540W

Quote:
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.


5 A x 3= 15 A .....( you've already blown it, sorry...)

[This message has been edited by sparky (edited 09-14-2002).]
Top
#81724 - 09/14/02 05:53 PM Re: 210.23(A)(2)
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Minor program notes...

"Keyless" for these lampholders means "sans pull-chain switch."

A "suicide adapter" refers to one with the plainly visible green-wire tail that could readily contact the adapter's male ungrounded blade and "heat up" an otherwise floating [but intended to be grounded] appliance case. Nowadays, the connection is a rigid-metal forked tab. IIRC, either type of adapter has never been permitted in Canada…id est, if you have a u-ground cord cap, it must be plugged only into a u-ground receptacle. {Corrections gladly accepted.}




[This message has been edited by Bjarney (edited 09-15-2002).]
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 99 Guests and 19 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals