#81458 - 08/19/02 11:05 AM converting T12 lamps to T8 lamps??
All Lites Offline
Junior Member
Registered: 08/16/02
Posts: 2
Loc: Van Nuys, Ca. USA
What I have exsisting is a 4 lamp 4 foot fixture with two magnetic ballasts. As it is now, they are switched, 2 lamps per switch. I'm converting it over to a electronic ballasts. Can I use a single electronic to run all four lamps as opposed to running two ballasts switched? Or is there a code that I have to keep them switched? Thanks in advance for any help offered. I'm in CA btw.
Top
2017 / 2014 NEC & Related Books and Study Guides
#81459 - 08/19/02 01:33 PM Re: converting T12 lamps to T8 lamps??
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
AllLites:
It's common here to install 1-4lite T8, F32 ballast to replace 2-2lamp T12 F40 (F34) ballasts.
CA may have an energy code, requiring "split wired" fixtures.
It's best to check with the local AHJ, or utility Co.
HotLine1
John
_________________________
John
Top
#81460 - 08/19/02 02:28 PM Re: converting T12 lamps to T8 lamps??
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
All - CA does have their Title 24 - Energy Conservation code requirements - (this is a large body of law covering lots of areas - I don't have the particular legal citation but any bldg. dept. will have that information for you ) this 'split' switch is a requirement.
Top
#81461 - 08/19/02 04:48 PM Re: converting T12 lamps to T8 lamps??
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Contact me via e-mail and I can give you some links for Title 24.

Basically you will need to retain "Bi-Level" switching, which cuts 1/2 the lighting power [half of the total lights per room or area].
This can be done by either using 2 lamp ballasts in each fixture, or creating a "Checkerboard" making every other fixture on the opposite switch. Checkerboard method allows you to use 4 lamp ballasts, but does not end up as uniform as the "A/B Per Fixture" method does.

Sounds or maybe

Contact me via e-mail at:
dtbigred@pacbell.net

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#81462 - 08/20/02 08:13 AM Re: converting T12 lamps to T8 lamps??
All Lites Offline
Junior Member
Registered: 08/16/02
Posts: 2
Loc: Van Nuys, Ca. USA
Thanks gentlemen! Scott you have mail
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals