#81416 - 08/12/02 11:48 AM Insulation Resistance
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
From Norm Koon:

I have a question concerning cables that are approximately 45 years old.

The insulation resistance test read as follows:

Air Temp 82 deg F
One Minute Megohm readings Ph A 1220 Ph B 2540 Ph C 484
Ten Minute Megohm readings Ph A 1470 Ph B 4100 Ph C 510
PI Index Ph A 1.11 Ph B 1.61 Ph C 1.05

Given this test data, would it be advisable to reuse these cables?

These cables are partly running underground, inside a basement and outdoors, so
an accurate temperature reading was not used. The temperature is only the outside
air temperature. Also they are still hooked up to the primary bushings of the transformer.

So they are not true readings of the cables. I was wondering if the disparity of the readings could be due to leakage on the transformer bushings. The test voltage was 2500 vdc. The system voltage is 6900 volts ac.
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#81417 - 08/12/02 01:21 PM Re: Insulation Resistance
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
"...still hooked up to the primary" should make individual readings meaningless, unless I misinterpreted something.
Top
#81418 - 08/12/02 01:34 PM Re: Insulation Resistance
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Norm
The 2500 volt DC test does not provide an adequate check of the insulation integrity.
Is the cable in use now? I would want to Hi Pot test the cable. New 15 kv cable is tested at about 60 kv but that is not what you want on cable this old. Check with the mfg annd see if they can give you a value to test the cable.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals