The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (Tjia1981, sparkyinak), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#81253 - 07/29/02 04:45 PM Main G.E.C used also as an E.G.C
cthusky Offline
Junior Member

Registered: 02/12/02
Posts: 6
Loc: South Windham Ct, USA
Senerio: Contractor does a 100 amp to 200 amp service upgrade to a single family home. The meter, and 100 amp panel, were located in the basement. The new meter is now located outside of the garage,and a new 200 amp panel is located on the inside wall of the garage. The old panel was left in the basement as a subpanel. The contractor fed the old panel with pvc from the new 200 amp panel. In the pvc are the two ungrounged legs, the neutral,and the main grounding electrode/equipment grounding conductor(one wire which hits a lug on the ground bar{neutral is isolated} then proceeds through the panel to the water meter located a couple feet away).Here's my question. Can the main g.e.c also be used as a e.g.c? I know system grounding is different then equipment grounding, but besides by definition is there an applicible article in the code I can refer to?

2014 / 2011 NEC & Related Books and Study Guides
#81254 - 07/30/02 03:16 AM Re: Main G.E.C used also as an E.G.C
sparky Offline

Registered: 10/18/00
Posts: 5545
if in fact, this is a detatched garage, then both structures would require a GEC, and GE's, and the conductor you mention bettween panels would merely be the EGC.

#81255 - 07/30/02 04:32 PM Re: Main G.E.C used also as an E.G.C
cthusky Offline
Junior Member

Registered: 02/12/02
Posts: 6
Loc: South Windham Ct, USA
Sparky, no this is an attached garage.

#81256 - 07/30/02 10:08 PM Re: Main G.E.C used also as an E.G.C
Steve T Offline

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
I don't believe anything in the NEC says this can't be done. Just have to make sure you are not setting up parallel neutral paths with incorrect bonding in the sub panel.

#81257 - 08/01/02 02:25 PM Re: Main G.E.C used also as an E.G.C
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
As long as the grounding electrode conductor is continuous and the grounded conductor is not bonded to the grounding conductor, I see no problem with the installation.