The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
51 minutes 42 seconds ago
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#81248 - 07/29/02 01:48 PM NEC Article 430
ongmark Offline
Junior Member

Registered: 07/29/02
Posts: 2
Loc: Salem, OR, USA
Minimum size branch circuit for (1) 15HP, 208v, 3phase, design letter "B", operating at 80% power factor.
I know the process, however the design letter and PF are throwing me?

Any help would be greatly appreciated.

2014 / 2011 NEC & Related Books and Study Guides
#81249 - 07/29/02 02:03 PM Re: NEC Article 430
sparky Offline

Registered: 10/18/00
Posts: 5545
do you actually have a 'B'motor?

[This message has been edited by sparky (edited 07-29-2002).]

#81250 - 07/29/02 03:02 PM Re: NEC Article 430
ongmark Offline
Junior Member

Registered: 07/29/02
Posts: 2
Loc: Salem, OR, USA

#81251 - 07/29/02 03:59 PM Re: NEC Article 430
3 Way Offline
Junior Member

Registered: 07/29/02
Posts: 6
Loc: TX

for one motor on the branch...
size branch circuit @ 125% of motor full load amps as listed in NEC 430.150.
15HP @ 208V 3ph ==> 46.2 amps
125% ==> 57.8 amps
select wire (after derations) for 57.8 amps

the design letter "B" is used for selecting overload protection
PF=80% is typical for induction motors but has no bearing on wire size. NEC table 430.150 has PF allowances "built-in" for induction motors.

hope this helps.

#81252 - 08/08/02 01:26 PM Re: NEC Article 430
Dan Neeser Offline

Registered: 03/12/02
Posts: 29
Loc: St. Louis, MO, USA
I think your question has been answered, but just an fyi.

A good reference tool that we provide is in the Bussmann SPD. See 84-99 for the Motor Circuit Table that shows the sizing required. The link for the SPD is below, below that is the link for other pubs and articles.