#81248 - 07/29/02 01:48 PM NEC Article 430
ongmark Offline
Junior Member
Registered: 07/29/02
Posts: 2
Loc: Salem, OR, USA
Minimum size branch circuit for (1) 15HP, 208v, 3phase, design letter "B", operating at 80% power factor.
I know the process, however the design letter and PF are throwing me?

Any help would be greatly appreciated.
Top
2017 / 2014 NEC & Related Books and Study Guides
#81249 - 07/29/02 02:03 PM Re: NEC Article 430
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
ongmark,
do you actually have a 'B'motor?

[This message has been edited by sparky (edited 07-29-2002).]
Top
#81250 - 07/29/02 03:02 PM Re: NEC Article 430
ongmark Offline
Junior Member
Registered: 07/29/02
Posts: 2
Loc: Salem, OR, USA
Yes
Top
#81251 - 07/29/02 03:59 PM Re: NEC Article 430
3 Way Offline
Junior Member
Registered: 07/29/02
Posts: 6
Loc: TX
ongmark,

for one motor on the branch...
size branch circuit @ 125% of motor full load amps as listed in NEC 430.150.
15HP @ 208V 3ph ==> 46.2 amps
125% ==> 57.8 amps
select wire (after derations) for 57.8 amps

the design letter "B" is used for selecting overload protection
PF=80% is typical for induction motors but has no bearing on wire size. NEC table 430.150 has PF allowances "built-in" for induction motors.

hope this helps.
Top
#81252 - 08/08/02 01:26 PM Re: NEC Article 430
Dan Neeser Offline
Member
Registered: 03/12/02
Posts: 29
Loc: St. Louis, MO, USA
I think your question has been answered, but just an fyi.

A good reference tool that we provide is in the Bussmann SPD. See 84-99 for the Motor Circuit Table that shows the sizing required. The link for the SPD is below, below that is the link for other pubs and articles.
http://www.bussmann.com/library/docs/Spd.pdf http://www.bussmann.com/apen/pubs/
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals