#81248 - 07/29/02 04:48 PM NEC Article 430  
ongmark  Offline
Junior Member
Joined: Jul 2002
Posts: 2
Salem, OR, USA
Minimum size branch circuit for (1) 15HP, 208v, 3phase, design letter "B", operating at 80% power factor.
I know the process, however the design letter and PF are throwing me?

Any help would be greatly appreciated.


2017 / 2014 NEC & Related Books and Study Guides

#81249 - 07/29/02 05:03 PM Re: NEC Article 430  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
ongmark,
do you actually have a 'B'motor?

[This message has been edited by sparky (edited 07-29-2002).]


#81250 - 07/29/02 06:02 PM Re: NEC Article 430  
ongmark  Offline
Junior Member
Joined: Jul 2002
Posts: 2
Salem, OR, USA
Yes


#81251 - 07/29/02 06:59 PM Re: NEC Article 430  
3 Way  Offline
Junior Member
Joined: Jul 2002
Posts: 6
TX
ongmark,

for one motor on the branch...
size branch circuit @ 125% of motor full load amps as listed in NEC 430.150.
15HP @ 208V 3ph ==> 46.2 amps
125% ==> 57.8 amps
select wire (after derations) for 57.8 amps

the design letter "B" is used for selecting overload protection
PF=80% is typical for induction motors but has no bearing on wire size. NEC table 430.150 has PF allowances "built-in" for induction motors.

hope this helps.


#81252 - 08/08/02 04:26 PM Re: NEC Article 430  
Dan Neeser  Offline
Member
Joined: Mar 2002
Posts: 29
St. Louis, MO, USA
I think your question has been answered, but just an fyi.

A good reference tool that we provide is in the Bussmann SPD. See 84-99 for the Motor Circuit Table that shows the sizing required. The link for the SPD is below, below that is the link for other pubs and articles.
http://www.bussmann.com/library/docs/Spd.pdf http://www.bussmann.com/apen/pubs/



Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 208
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7654 MB (Peak: 0.9026 MB) Zlib enabled. Server Time: 2017-03-28 23:34:00 UTC