#81191 - 07/17/02 04:10 PM EMT mounted on the floor.
electrician02125 Offline
Member
Registered: 02/01/01
Posts: 90
Hello,

Can you install emt on the floor?

I have a computer lab that has concrete slab floor and ceiling yet very cheap/weak partition sheetrock walls enclosing the space. The lab needs power. I have used pancake wiremold in the past and I am not very fond of it.

I want to run the emt on the slab in the corners (where it is not subject to extreme physical damage) along the base of the sheetrock walls but mounted on the concrete slab floor.

I cannot find anything that prevents me from doing this in the NEC.

Any help is appreciated.
Top
2017 / 2014 NEC & Related Books and Study Guides
#81192 - 07/17/02 04:32 PM Re: EMT mounted on the floor.
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
If corrosion from floor contact is not of concern and the run does not create a tripping hazard, it should be OK.
Top
#81193 - 07/17/02 04:43 PM Re: EMT mounted on the floor.
jlhmaint Offline
Member
Registered: 05/25/02
Posts: 208
Loc: Fredericktown, OH, U.S.A
we have alot of over head cranes in our shop and we run emt (rigid) across the floor all the time to get to equipment but you also have to take into account what Bjarney said.
Top
#81194 - 07/17/02 05:20 PM Re: EMT mounted on the floor.
electrician02125 Offline
Member
Registered: 02/01/01
Posts: 90
Makes sense to me.

Thanks Guys.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 72 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals