Our main building has a 120/208 Volt, 3Ph, 4W. electric service. We would like to install a panelboard in a remote building. It does not have any 3Ph. loads. According to the NEC must a 120/208 Volt, 3Ph, 4W. panelboard be installed in remote building or would a 120/208 Volt 1Ph. panel be compliant?
Top
Work Gear for Electricians and the Trades
#8119 - 03/08/02 10:02 AM Re: Remote Building
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Frank,
That is a design issue and not covered by the code. If you do this please remember that all neutral conductors will be current carrying for derating purposes.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#8120 - 03/08/02 11:06 AM Re: Remote Building
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Thanks for reply Don. The only thing I found in the NEC that was even a little bit related, if at all was Article 210.11(B) "Load Evenly Proportioned Among Branch Circuits".
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 64 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals