#81054 - 06/20/02 10:57 PM SE cable?
ravin Offline
Junior Member
Registered: 06/20/02
Posts: 6
Hello, I installed and elec. service with the meter can and panel practically back to back within the same partion, I used SE cable due to the meter elevation to panel knock outs not in line with each other; the inspection failed due the inspectors reasoning that since the cable is unfused, it can't be inside a partion. Builder had to build out into room a deeper wall to facilitate the use of PVC conduit in lieu of SE cable. Should I have challanged his ruling. Any thoughts on this Thank you.
Top
2017 / 2014 NEC & Related Books and Study Guides
#81055 - 06/21/02 05:53 AM Re: SE cable?
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Ravin,
230-70(a) says it shall be installed as near as practicable. That is the only thing the NEC says on the subject, which leaves distances up to local interpretation.

In VA each county is allowed to set that distance, most of them pick 7 feet. If it is back to back (or nearly so, as you indicate) it would be allowed here. BUT you may not be here

Suggest you call your local chief electrical inspector to ask what the interpretation is, an how far you're allowed to enter the building. This is an old argument, and I'm guessing they've already addressed it.

Personally, I don't think there is much 'structural' difference between the pvc and the sec.
Top
#81056 - 06/21/02 05:27 PM Re: SE cable?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
ravin,

Is this a 2x4 studded wall?

What you describe is common practice around here, but in reality there is not much to protect that cable and rather impossible to keep larger SE cables a safe distance away from finished surfaces in a 2x4 wall. It wouldn't surprise me if that was what they are concerned about. Just a guess.

Bill
Top
#81057 - 06/22/02 09:30 PM Re: SE cable?
ravin Offline
Junior Member
Registered: 06/20/02
Posts: 6
No Bill, the wall is 2x6, I've done many that way also; seems this inspection was based on what ifs. Thanks for response.
Top
#81058 - 07/01/02 08:53 PM Re: SE cable?
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
se cable to the next full stud bay, or even the first full stud bay around a corner, would be acceptable here in oregon.....

when you say "same partion," i assume you mean "same partition," and assume you are refering to the "same stud bay" within a partition? which would be way ok here
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals