#8104 - 03/07/02 05:54 PM GFCI circuit for sump pump
menegt Offline
Member
Registered: 01/09/02
Posts: 35
Loc: sacramento, ca
Sorry for the ignorance people but, our University just built this fancy fountain.

The sump pump along w/ the controls, timer and pump related equip are in a underground vault.

It just rained recently and the GFCI circuit for the sump pump had tripped. Water was almost to the controls. I suggested calling
back the contractor to replace sump pump. Contractor says there was a surge that took place?!(*&^(

Is the motor on a sump pump (or any single phase motor) that is on a GFCI circuit supposed to have a certain rating/designation/efficiency? This has happened a few times already.

Appreciate the help. Great site.
IBEW 340 - Mike
Top
Work Gear for Electricians and the Trades
#8105 - 03/07/02 07:08 PM Re: GFCI circuit for sump pump
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
What is the reasoning behind the sump pump being on a GFCI?
Top
#8106 - 03/07/02 08:47 PM Re: GFCI circuit for sump pump
menegt Offline
Member
Registered: 01/09/02
Posts: 35
Loc: sacramento, ca
sorry, i meant GFI circuit. It's coming off a GFI breaker w/ a GFCI receptacle on the same circuit.
Top
#8107 - 03/08/02 04:32 AM Re: GFCI circuit for sump pump
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
What I'm saying is, I don't beleive the sump pump is required to be, or should be, on a GFI.
Top
#8108 - 03/09/02 07:08 PM Re: GFCI circuit for sump pump
menegt Offline
Member
Registered: 01/09/02
Posts: 35
Loc: sacramento, ca
When running a submersable pump for a fountain the pump is required to be on a GFI.
680-51
Top
#8109 - 03/10/02 04:01 AM Re: GFCI circuit for sump pump
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Are we talking about two different pump motors? The decorative fountain pump motor is required to be GFCI protected. A sump pump (ejector pump) is not required to be GFCI protected.
Top
#8110 - 03/11/02 05:26 PM Re: GFCI circuit for sump pump
menegt Offline
Member
Registered: 01/09/02
Posts: 35
Loc: sacramento, ca
Frank, can you direct me to where in the code that it says that a sump pump for a fountain not be GFI protected? This is an in ground vault about 5' deep containing the fountain pump, fiber optic lighting and controls for the fountain. Thanks.
Top
#8111 - 03/11/02 05:44 PM Re: GFCI circuit for sump pump
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Mike,

I think there's a bit of confusion over what type of pump you are talking about. When I hear 'sump pump' I think of a pump that is installed to prevent flooding, or an ejection pump. It operates on a float switch which turns the pump on when water rises to a certain level. I'm reasonably sure that this is what Frank and Redsy are referring to.

Is that what you mean? Or are you referring to a pump that shoots the water in the air for the fountain?

Bill
Top
#8112 - 03/12/02 05:24 PM Re: GFCI circuit for sump pump
menegt Offline
Member
Registered: 01/09/02
Posts: 35
Loc: sacramento, ca
In the vault there is a sump pump that prevents flooding of the vault. It has a float used to switch on the sump pump. There is a pump that cirulates water and pumps water into the fountain. My problem is that when the sump pump circuit which is on a GFI circuit trips, the controls are in danger of water damage (if the water level gets that high). Is there a certain motor I should use on a GFI circuit? Code says that the sump pump has to be on a GFI circuit. Actually the fountain pump (for pumping water into the fountain) has to be on a GFI circuit also. Thanks.... Mike
Top
#8113 - 03/13/02 04:18 AM Re: GFCI circuit for sump pump
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I don't believe the intention of 680.51(A) requires you to include your sump pump as a part of "fountain equipment".
The submersible pump they refer to is a pump that would sit at the bottom of the reservoir that is filled with the water that you are circulating through your fountain.
I think you can remove the GFCI from the sump pump.

[This message has been edited by Redsy (edited 03-13-2002).]
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (geoff in UK), 79 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals