#81022 - 06/16/02 09:44 AM MLO panels as service equipment.
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
In another forum I suggested the use of a twelve slot, single phase, main lug only panel as a way of heavying up an existing multi panel installation. I proposed supplying each of several "sub panels" from a breaker in the new service equipment and converting the original service panel from a breaker in the new service equipment after converting it to a lighting and appliance panel board by installing an equipment grounding buss and removing the neutral buss bonding screw.
The problem one inspector on that forum had was that the MLO panels I am talking about using as service equipment can except single pole breakers. He said he would turn down the installation on the grounds that more than six breakers could be installed. An example of the kind of panel I am talking about is a Square D QO112L200GRB. These panels are listed as service equipment. The label reads "suitable for use as service equipment when not more than six main breakers are installed and not used as a lighting and appliance panel board. My approach is to use no breaker under forty amps with a neutral connection in the circuit in the service panel. That means that thirty amp water heater circuits and twenty ampere heater circuits are cool in the service panel but thirty ampere dryer circuits have to go in the panels that are fed from the service.
I have used this approach to heavy up a number of services and I have not had any problem. The inspections all went without a hitch. The reason for asking this question here is that if this one inspector represents a substantial sector of opinion I will take the precaution of getting these installations approved in advance so as to avoid any problem on inspection.
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
2017 / 2014 NEC & Related Books and Study Guides
#81023 - 06/18/02 05:57 PM Re: MLO panels as service equipment.
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
tdhorne,

What you propose is accepted practice in the State of Nebraska. Nothing in the NEC prohibits this AFAIK. Everything is open to interpretation by the AHJ.......

Probably it's not worth fighting a battle over. Just get a main-breaker panel, it's a cleaner, safer installation.

GJ

[This message has been edited by golf junkie (edited 06-18-2002).]
Top
#81024 - 06/19/02 06:00 AM Re: MLO panels as service equipment.
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
I might buy cleaner but I won't buy safer. One of the types of properties I use this in is rural residential properties with well pumps. By using an MLO panel to supply the interior panel, the well, other buildings, air conditioning, and so forth I assure that a problem in any one building will not deprive the occupants of the water to fight a fire with until their rural fire department has time to respond. I am aware that the code allows a separate disconnect for that purpose but that adds markedly to the expense of the installation.
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#81025 - 06/20/02 07:26 PM Re: MLO panels as service equipment.
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
Sounds like you are building a new service, and using the old service equipment as a subpanel. If your new panel is service rated, and we all know the "6 switch on services" rule, I don't see what the inspector's problem is. To me it doesn't matter that more that 6 breakers could be installed. What matters is, that you install 6 breakers or less. We all know that only trained persons will be working on this equipment, and if a person is trained they should know the "6 switches or less" on services rule. So, the inspector can't assume (and we all know what happens when we assume things, it makes an a$$ out of u and me) that someone is going to, at some time in the future, break the rule by adding another breaker. Sounds like a job for Sam Colt.
No offense to any inspectors out there, or to you junkie. By the way, junkie, how's your game?

At your Service,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
#81026 - 06/21/02 03:00 PM Re: MLO panels as service equipment.
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Inspections should address what is, not what could be IMO.
He/She could just as easily fail my 40 cir. cans on the same premis here.

chapter & verse please....
Top
#81027 - 06/21/02 03:19 PM Re: MLO panels as service equipment.
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Tom, this guy and his (I AM GOD) attitude is completely out of line. With the right person involved, say one that had the means and time to sue him and his city or county for lost revenues and inconveniece, I would bet he would reevaluate his "rule making" and go back to enforcing the code as it is written. or at least someone above him would see that he did. IMO BTW I read that thread in it's entirety, and you out classed him

Roger

[This message has been edited by Roger (edited 06-21-2002).]

[This message has been edited by Roger (edited 06-21-2002).]
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals