#80909 - 06/10/02 03:07 PM Horse piddle
Rabbit Offline
Member
Registered: 01/01/02
Posts: 61
Loc: Kingsport Tennessee
Am coming out of the main switch gear in a hospital with a 480v 150a feed. The gear is in the basement. This will feed a new 208/120 panel on the 3rd floor via a transformer, also on the 3rd floor. The print shows the feeder going strait to the trans. Don't I need a disconnect here? Panel is main brkr. Also this panel will serve some isolated ground circuits. Does the ig have to go all the way back to the gear or can it stop at the trans? Articals?
Top
2017 / 2014 NEC & Related Books and Study Guides
#80910 - 06/10/02 03:36 PM Re: Horse piddle
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
There is not a code requirement to have a disconnect at the transformer. The transformer primary does require an OCPD, but that can be at the main gear and provide the required protection for both the feeder conductors and the primary side of the transformer. As for your isolated grounds look at 250.146(D). They must trerminate at a point where they can clear any ground fault. For your SDS, that would be at the same point where you connect the grounding electrode conductor for the secondary of the transformer.
Don

[This message has been edited by resqcapt19 (edited 06-10-2002).]
_________________________
Don(resqcapt19)
Top
#80911 - 06/10/02 05:39 PM Re: Horse piddle
dlabrenz Offline
Member
Registered: 09/04/01
Posts: 25
Loc: Muskegon, MI
I would think that a disconnect would be required to protect the secondary conductors.
240-21(c)(1) seems to indicate that the secondary conductors are not protected by the primary OCPD, and I am not sure that I would like unprotected conductors running 3 floor til they get to the mail in the load center.
Top
#80912 - 06/10/02 06:39 PM Re: Horse piddle
Rabbit Offline
Member
Registered: 01/01/02
Posts: 61
Loc: Kingsport Tennessee
Thanks Don. This is my first hospital and it just didn,t look right. I will proceed.
Dlabrenz, the conductors are protected at the switch gear, approx. 150 ft.
Top
#80913 - 06/10/02 07:39 PM Re: Horse piddle
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
dlabrenz,
The main in the panel can provide the required protection of the secondary side of the transformer and the secondary conductors. This may involve the use of the "tap" rules that will limit the length of the secondary conductors.
Don
_________________________
Don(resqcapt19)
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals