#80866 - 06/09/02 10:31 AM derate Q
Eandrew Offline
Member
Registered: 05/24/02
Posts: 68
Loc: seattle, wa, usa
If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?
Top
2017 / 2014 NEC & Related Books and Study Guides
#80867 - 06/11/02 12:54 PM Re: derate Q
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
You must use the derating for continous
load and conduit fill when derating these conductors.
Top
#80868 - 06/11/02 02:29 PM Re: derate Q
Eandrew Offline
Member
Registered: 05/24/02
Posts: 68
Loc: seattle, wa, usa
Thanks Bob.