The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 82 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80866 - 06/09/02 10:31 AM derate Q
Eandrew Offline
Member

Registered: 05/24/02
Posts: 69
Loc: seattle, wa, usa
If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?

Top
2014 / 2011 NEC & Related Books and Study Guides
#80867 - 06/11/02 12:54 PM Re: derate Q
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
You must use the derating for continous
load and conduit fill when derating these conductors.

Top
#80868 - 06/11/02 02:29 PM Re: derate Q
Eandrew Offline
Member

Registered: 05/24/02
Posts: 69
Loc: seattle, wa, usa
Thanks Bob.