#80848 - 06/07/02 12:41 PM Delta Skelter
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I am stumped here. There is a 3 ph 4 wire panel, voltages to G are 120,120,240.
There re only two X-formers on the pole, the bracket is visible where the third can may have been....
Top
2017 / 2014 NEC & Related Books and Study Guides
#80849 - 06/07/02 01:30 PM Re: Delta Skelter
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Sparky,
Sounds like an open delta with a wild leg, but the 240 to g should be closer to 208.
Don
_________________________
Don(resqcapt19)
Top
#80850 - 06/07/02 01:43 PM Re: Delta Skelter
ameterguy Offline
Member
Registered: 05/17/02
Posts: 30
Loc: Mass
Sparky,

I agree with Don, delta, with center tap. Usually you should get:
a - g 120
b- g 120
c - g 208

a- b 240
a- c 240
b- b 240

What are your phase to phase voltage readings?
Top
#80851 - 06/07/02 03:36 PM Re: Delta Skelter
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Top
#80852 - 06/08/02 04:21 AM Re: Delta Skelter
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
ameterguy,
the readings are as you've stated.sorry 'bout that...
( 'twas a dark rainy night, etc, etc..) The high leg is marked white, removing the panel cover is like taking the bra off the fat lady....


Roger, yep that's the beast.. is the grounding conductor common to the primary??

Top
#80853 - 06/08/02 05:36 AM Re: Delta Skelter
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sparky, The grounding conductor could be common to both. The real caution here would be lets say you were going to make this installation verses the utility. If your primary were an ungrounded delta and you were going to provide a grounded system, the grounding would have to be isolated on the secondary side.

Roger
Top
#80854 - 06/08/02 07:34 AM Re: Delta Skelter
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
There one more variation of the open-delta arrangement used by electric utilities, and fairly common in some areas—that is open-wye grounded primary, open-delta secondary. At: http://www.elec-toolbox.com/usefulinfo/xfmr-3ph.htm you can visualize it looking at Fig.1-1 Y-∆ layout. Now remove the primary winding at the ten o’clock position that is connected to L2. The hi-side wye point has to be connected to the hi-side neutral conductor [not shown on 1-1.] so there are still three conductors serving on the primary side of the bank. Now, on the secondary, delete the winding at the 2 o’clock position. [Sometimes this is incorrectly called ‘two-phase,’ but that designation is reserved specifically for 90° phase-displaced voltages.]

In areas where the multigrounded common neutral is used, it saves a fused cutout and wire for the unneeded third phase. {For geeks only—In some areas where lo-side delta voltages are needed, a grounded wye-delta bank is prohibited, for it acts as an undesirable ground source and can induce high currents in the common-neutral conductor during hi-side faults.}


[This message has been edited by Bjarney (edited 06-08-2002).]
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals