#80778 - 05/21/02 05:22 PM A dedicated EGC run in a separate raceway
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Hello:

I am installing a new elevator controller on the top of a 23 story building that requires a dedicated equipment grounding conductor that will be run back to the service equipment location. Running this EGC, with the existing phase conductors is not possible without first removing them. The raceway is a 3 inch Rigid Galvanized Steel Conduit, and appears to be a good grounding path with no corrosion, and all fittings are tight.

I have a spare conduit that runs along this conduit that I would like to use.

This appears to be a code violation per Article 250, but I wonder if the CMP is referring to the service conductors, and not to an equipment ground.

I am aware that the impedance of the system may be higher if I do this.

Is this allowable?

Thanks,

Peter Volpe
Electrical Engineer


[This message has been edited by Joe Tedesco (edited 05-21-2002).]
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#80779 - 05/21/02 07:15 PM Re: A dedicated EGC run in a separate raceway
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
I haven't seen the 2002 version, but Phillip Simmons' Soares Book on Grounding on the uses and abuses of grounding has been outstanding.
Top
#80780 - 05/22/02 03:23 AM Re: A dedicated EGC run in a separate raceway
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Peter,
You did not say if the service is a separate service or not. Most elevator rooms I've done are so we will assume this one is also.

You can install an equipment ground in it's own conduit. Yup it raises the impedance WAY high in this case but don't forget, it plays almost no role in fault clearing at any rate, it's only there as a 0 point reference.

My big question is WHY do you need one running all the way back down to, I assume, the building grounding electrode from the 23rd floor? Is there no building steel? In lieu of that, is there no grounding electrode in the closets for xfrmr reference?

If elevator equipment is that sensitive, this stuff is doomed anyway, or are the elevator people becoming like computer people, you know "Our stuff is special".

Good luck.
Top
#80781 - 05/22/02 07:43 AM Re: A dedicated EGC run in a separate raceway
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
George,
This is an EGC not a grounding electrode conductor and it will carry the fault current. I don't see any exceptions even for an isolated EGC. It is required by 250.134(B) and 300.3(B) to be in the same raceway as the power conductors. If the circuit is above 200 amps or so, the additional inductive reactance of an EGC in a second matallic raceway may very well be high enought so that the OCPD does not open.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#80782 - 05/23/02 07:03 AM Re: A dedicated EGC run in a separate raceway
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Don,
OOOOOOPS, I did get that wrong. agreed
Top
#80783 - 05/24/02 09:34 PM Re: A dedicated EGC run in a separate raceway
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
If this is an IGC [Isolated Grounding Conductor] I think you could run it separate from the Subfeeder or Branch Circuit's Conduit and comply with the NEC.

The "Gurus Of The NEC" have the answers, whereas I only have suggestions and thoughts.

Scott S.E.T.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#80784 - 05/25/02 06:07 AM Re: A dedicated EGC run in a separate raceway
Gwz Offline
Member
Registered: 04/29/02
Posts: 197
Scott,

Doesn't 250.146(D) Say " - - - run with the circuit conductors. - - - ." ?

The basic rule of 250.134(B) is not altered by the word " Isolated " of 250.146(D) which is part of 250.146 Section.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals