#80760 - 05/15/02 12:28 PM Transformer as a raceway?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Question from:

Theodore P. Von Sydow
US. Department of State

My question in a nutshell: Can a conductor pass through a transformer if it is not connected to the transformer?

Can the transformer be used as a raceway for a circuit or conductor that is not directly related to the function of the transformer?

Thank you
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#80761 - 05/15/02 05:40 PM Re: Transformer as a raceway?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
If there is no violation of voltage class' of insulation, or type of wiring (communications, fire alarm, etc), seems ok.
_________________________
Ron
Top
#80762 - 05/16/02 04:20 AM Re: Transformer as a raceway?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
This is not a good practice.
If the transformer fails, you would have to remove the conductor and disrupt it's loads in order to replace the transformer.
Top
#80763 - 05/16/02 05:47 AM Re: Transformer as a raceway?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
I agree, no foreign wires are to be passed through the transformer. I expect that there will be many who wear the AHJ hat that will agree. It is also common knowledge that all conductors are not to be passed through an area that originates in the top section -- the label in the transformer enclosure will cleary identify this and other restrictions.
_________________________
Joe Tedesco, NEC Consultant
Top
#80764 - 05/16/02 08:39 PM Re: Transformer as a raceway?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
I also agree, not a good practice. I think the original questions infers that the poster wants to know if it is a code violation. I don't find a violation.
_________________________
Ron
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 119 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals