#80721 - 05/14/02 02:55 PM switch by shower
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Can a switch be within reach of a shower door/curtain?
Top
2017 / 2014 NEC & Related Books and Study Guides
#80722 - 05/14/02 04:40 PM Re: switch by shower
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Sparky,
The code only says it can't be in the shower space. It is permitted to be within reach.
Quote:
404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#80723 - 05/15/02 10:57 AM Re: switch by shower
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
A rare case of our "code" being stricter than the NEC!

No switch here is allowed to be within reach of anyone in a bath or shower, unless it's a ceiling-mounted cord pull type.

'66 has a pic on his site of a switch within easy reach of someone in the tub.



[This message has been edited by pauluk (edited 05-15-2002).]
Top
#80724 - 05/15/02 07:22 PM Re: switch by shower
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Paul, the pic you speak of was presented in a thread here as well.

Click Here!

What about sconce lights?

I've actually installed a pair of sconces in the tub space in the last two houses I've wired. It was in the plans, and I can't find anything in the NEC to prevent it. They are on GFCI protection, however.
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#80725 - 05/16/02 12:01 PM Re: switch by shower
motor-T Offline
Member
Registered: 11/10/01
Posts: 280
Loc: Girard, Ohio, USA
'66
Actually there is a code reference for your sconces actually not the sconces but in reference to :

(3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets.

Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A).

.. So the sconces are ok, as far as I cant tell as long as it does not exceed 50 %(210-23)..

-Mark-
Top
#80726 - 05/16/02 03:01 PM Re: switch by shower
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Pardon my ignorance, but what exactly is a sconce light? (I seem to be lost mid-Atlantic in terminology again!)

Virgil,
Completely off-topic....
Loved reading your happy/sad story about Murphy. I adore cats myself, and I know the feelings you go through when you loose such a friend.
Top
#80727 - 05/16/02 04:22 PM Re: switch by shower
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Paul,
it's generally considered a fixture ( luminare) that mounts to the wall instead of the cieling.....


there would seem a bit of confusion ( mostly on my part) as to the 'shower space' which is 8' above and 3' surrounding the tub rim, as opposed to the space within the shower itself.
Top
#80728 - 05/16/02 09:06 PM Re: switch by shower
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Thanks Paul, up to 6 dogs and 7 cats now, the pets section on my web site needs updated...

Dern critters are eatin' me out of house and home!

But I love 'em all...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#80729 - 05/16/02 10:50 PM Re: switch by shower
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Top
#80730 - 05/17/02 07:20 AM Re: switch by shower
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Wow, that's some managerie Virgil! Only one cat here at the moment; rescued him as a kitten in Ireland about 3 years ago. Lost another after nearly 9 years to a heart defect -- It's so heartbreaking.

I guess I should have looked up "sconce" in the dictionary before. According to my Concise Oxford version:

Quote:

sconce: n. Flat candlestick with handle; bracket candlestick to hang on wall [Middle English from Old French esconse lantern, or from medieval Latin sconsa from Latin absconsa fem. p.p. (as n.) of abscondere hide.]


O.K., I live and learn. It makes sense now.



[This message has been edited by pauluk (edited 05-17-2002).]
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals