#80657 - 05/05/02 05:20 PM romex in small office?
silverbk Offline
Member
Registered: 02/24/01
Posts: 60
I have been contracted to wire a small free standing office one story wood on slab construction approx 25 x 25.

It looks like a romex job, but I have been told that the inspector wants MC cable. His reasoning that it is a place of assembly.

Bldg has it's own service and will be used a an office to rent self storage units.

With my understanding of the code single story commercial, romex is acceptable. Place of assembly means 100 people or more, and bx would now be accepatble there also.
Top
2017 / 2014 NEC & Related Books and Study Guides
#80658 - 05/06/02 04:45 PM Re: romex in small office?
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
first, i would speak to the inspector. then quote the code.

i think building construction dictates wiring methods..

take for instance a three story dormitory..this may be considered a place of assembly..it is built out of wood and wired with romex...i would be shocked if your inspector would require this building to be wired with a/c cable? even motels get romex..

i would use romex if the ahj will go along with it..if not a/c cable is not too bad but it is more expensive, time consuming and whole lot dirtier..

good luck

-regards

frodo
Top
#80659 - 05/07/02 04:30 AM Re: romex in small office?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I don't believe it to be a Place of Assembly.
I would like opinions on whether a commercial office complex that employed 300 people is considered a place of assembly.
I don't think so, because more than 100 people are not congregating in one area.(I wonder about a large area that holds more than 100, but has cubicles separating them) However a conference room or cafeteria in the same building that holds in excess of 100 people would be considered a place of assembly.
Please comment on the above situations.
Top
#80660 - 05/07/02 08:42 AM Re: romex in small office?
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
This is one inspector that has been standing out in the sun too long. He needs to take a look at NFPA 101 Life Safety Code.

Areas of assemblyof concentrated use allow for 7 sq ft per person which means only 89 would be allowed in your room (based on my really old copy). Not to mention that he has totally missed the boat on what a place of assembly is.

He could have a point about any wiring above a dropped ceiling though.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#80661 - 05/07/02 02:08 PM Re: romex in small office?
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
Redsy - "I wonder about a large area that holds more than 100, but has cubicles separating them"

Any room still must 'qualify' under other building code definitions to constitute a place of assembly. The building code and NEC lists those spaces that fall under areas that could qualify as places of assembly. A 12,000 sf room with 120 cubicles (100 sf load factor per code) does not become a place of assembly because there are more than 100 people in the room...it is still an office space.
Top
#80662 - 05/18/02 08:43 AM Re: romex in small office?
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
NEC 518.2(A) gives many examples of places of assembly. NM cable seems perfectly acceptable for "silverbk" application.

Frank
Top
#80663 - 05/18/02 09:12 AM Re: romex in small office?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
If you use NM cable, be careful of the new rule in 334.12.
Quote:
334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be used as follows: (1) As open runs in dropped or suspended ceilings in other than one- and two-family and multifamily dwellings.

Don(resqcpt19)
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals