The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#80647 - 05/04/02 06:52 PM 110.22 series mrkg
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
copied from 2002 nec:
110.22 Identification of Disconnecting Means.
Where circuit breakers or fuses are applied in compliance with the series combination ratings marked on the equipment by the manufacturer, the equipment enclosure(s) shall be legibly marked in the field to indicate the equipment has been applied with a series combination rating. The marking shall be readily visible and state the following:

CAUTION — SERIES COMBINATION SYSTEM
RATED ____ AMPERES. IDENTIFIED
REPLACEMENT COMPONENTS REQUIRED.

240.86 Series Ratings.
Where a circuit breaker is used on a circuit having an available fault current higher than its marked interrupting rating by being connected on the load side of an acceptable overcurrent protective device having the higher rating, 240.86(A) and (B) shall apply.
(A) Marking. The additional series combination interrupting rating shall be marked on the end use equipment, such as switchboards and panelboards.

then i copied this from bussmann:
As required in Section 110-22, the load-side panelboard/switchboard label shall be field marked with the short-circuit rating of the series combination, type circuit breaker for replacement, part number for the series rated line-side, feeder fuses and location/name of this fuse switch/panelboard/switchboard. The panel/switch with the line-side fuses shall be field marked with short-circuit rating of the series combination, part number for fuse replacement and the location/name of load-side, series rated panelboard/switchboard.

ok, but thats a lot of marking, so does everybody do this for every lighting panelboard?
or do you throw away the red sticker with the 110.22 blurb?
or do you mark the line-side series rating on the red sticker at the load and line panel locations?
or am i just really lost?

the lighting panel comes with specs attached that says the panel itself is rated for 65,000a at 240v max, so the panel is marked already, and now i am supposed to identify the max short circuit rating for the breakers in that panel? is that right?
Top
2017 / 2014 NEC & Related Books and Study Guides
#80648 - 05/05/02 07:32 PM Re: 110.22 series mrkg
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
We have no need to do those markings, because the series rating of the series rated equipment is never specified. Lowest AIC of the panel or combo is the fully rated AIC rating, then you don't have to do those series rating labels at all!
_________________________
Ron
Top
#80649 - 05/07/02 04:39 AM Re: 110.22 series mrkg
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Are you sure you are actually using lower rated equipment than the available fault current? (Installing a series-rated system)
Top
#80650 - 05/07/02 08:19 PM Re: 110.22 series mrkg
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
maybe i've missed the point. anyone have an example of where it would need to be marked?
Top
#80651 - 05/11/02 05:30 PM Re: 110.22 series mrkg
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
I think Ron means that if you use, for example, ALL 22KAIC molded-case breakers, then labeling would not be required.
Top
#80652 - 05/12/02 07:50 PM Re: 110.22 series mrkg
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
A lot of equipment comes with a labeled AIC rating on it's own (for fully rated), and a documented series rating if used with another particular peice of distribution overcurrent protection device. If you use a panelboard fully rated at 22KA and there is 15KA short circuit available, then no additional marking related to AIC is required, because you are using it within its fullt rated capabilities.
But, if you used that panelboard (fully rated at 22KA) and had a particular fused switch upstream (documented by manufacturer for series listing) the series rated AIC for the combination is 65KA and is acceptable for use on a cirucit up to 65kA (higher than 22kA). In this case, where the short circuit available is higher than the fault rated listing, you would have to label as you indicated, to be sure that no one will replace that particular fuse with a non-compatible fuse and relinquish the series rating of the combination, and thus leave the panelboard undersized relative to the short circuit interrupting capacity.
_________________________
Ron
Top
#80653 - 05/20/02 07:38 AM Re: 110.22 series mrkg
Dan Neeser Offline
Member
Registered: 03/12/02
Posts: 29
Loc: St. Louis, MO, USA
Cindy,

If you would like some additional information, please see my reply to GWZ on this topic and the additional information links for Bussmann information. Hopefully this will help.

Link for reply to GWZ: http://electrical-contractor.net/ubb/Forum7/HTML/000167.html

p.s. we also have a on-line training presetation (Interrupting Rating Review & Series Rating) on this topic. Check it out if you have a high speed internet access, because it is a large file (7.5Meg). See this link for it...http://www.bussmann.com/services/training/

Thanks,
Dan
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 76 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals