The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80579 - 04/29/02 07:11 AM Pool questions
Switcher Offline
Junior Member

Registered: 04/29/02
Posts: 9
Loc: Charlotte NC
New guy here,my background is in Industrial work and have recently decided to try a little residential on the side so please pardon my ignorance.

Now for the questions:

1. Pool pump 680.22 (5) requires GFCI protection for pool pump motors up to 240 volt....Do pool pumps (240v) come with a neutral connection? If not and they are straight 240v how can a 2 pole 20amp GFCI breaker trip with out a neutral connection???

2. Since an insulated ground in coduit is required to the pump motor to keep the equipment ground from picking up stray voltage, would it not apply to recpt/lighting circuits as well? In other words can you use UF and direct bury for lighting (up to wet niche j-box) and recepts around the pool?

Thanks in advance
Switcher

Top
2014 / 2011 NEC & Related Books and Study Guides
#80580 - 04/29/02 11:49 AM Re: Pool questions
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
A 2-pole GFI breaker compares the current between the 2 hot legs on a sraight 240 volt circuit. If one is less than the other, there must be leakage somewhere, and the GFI will trip.
_________________________
Peter

Top
#80581 - 04/29/02 11:56 AM Re: Pool questions
Switcher Offline
Junior Member

Registered: 04/29/02
Posts: 9
Loc: Charlotte NC
If pump is hardwired with a switch at pump does it still require GFCI?

Top
#80582 - 04/29/02 01:36 PM Re: Pool questions
C.Urch Offline
Member

Registered: 05/23/01
Posts: 36
Loc: Kill Devil Hills, NC USA
Yes, It still needs to be GFCI. You could wire the pump 115 Volts and cord and plug it into a GFCI receptacle. As for the pool light (wet niche) itself...it cannot be run in UF. You must have an insulated grounding conductor from your source (breaker) in conduit without a splice to the light. Some inspectors allow a splice at the switch but you will have to check with yours.

Top
#80583 - 04/29/02 01:39 PM Re: Pool questions
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Switcher,

You'd better ask the local inspector about the hardwired pump and if it needs GFCI protection (240v). He has the last word. As far as the UF goes, you cannot use it for the pool light or anything related with the pool. You really should go over all of this with the local AHJ before you get started if you have never done this before.

Bill

[This message has been edited by Bill Addiss (edited 04-29-2002).]

Top
#80584 - 04/29/02 03:26 PM Re: Pool questions
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Switcher,

If you can find a copy of the 2002 NEC Handbook, check it out, the drawings & explanations are really good.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#80585 - 04/29/02 03:57 PM Re: Pool questions
Switcher Offline
Junior Member

Registered: 04/29/02
Posts: 9
Loc: Charlotte NC
Thanks for the replies, unfortunately I do not have the 02 Handbook, just the regular codebook. I understand most of article 680, just wanted to clarify the above points.

The AHJ (from what I have been told by local pool guy) routinely passes UF for the entire installation, I was able to read enough to figure out that wasn't right.

The county in question is somewhat rural and apparently not very strict.... I just want to make sure it's right despite what AHJ says they will accept as a minimum.

Thanks again, very informative board, glad I found it.