The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80529 - 04/27/02 06:48 AM 3 phase sub panel ?
ken m Offline

Registered: 08/14/01
Posts: 61
Loc: south carolina
i hope to explain this question clearly.
a small fabrication shop has a 400 amp 240v 3 phase service. (currently 140 amp calc. load) The owner wants to expand the building which would require a 200 amp sub panel (calc. load 100 amps) The current panel (GE) will not accept a 200 amp breaker (load side)to feed the sub. Question is...would I be able to connect to the line side of the 400 amp main, which is double luged, to feed a 200 amp breaker adjecent to the main panel to feed the sub located about 60 feet away?
There is no disconnect @ the meterbase.
thx for any help. ken m

2014 / 2011 NEC & Related Books and Study Guides
#80530 - 04/27/02 06:25 PM Re: 3 phase sub panel ?
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
230-72 requires the disconnects to be grouped. Could you terminate under the extra set of lugs (main was double lugged) and land in an enclosed breaker (rated for service entry), then go onto the "sub panel"?

#80531 - 04/28/02 05:25 AM Re: 3 phase sub panel ?
ken m Offline

Registered: 08/14/01
Posts: 61
Loc: south carolina
yes ron, the enclosure to house the main for the sub could be mounted adjecent to the primary service panel. thx for the response, ken m