The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80503 - 04/23/02 12:22 PM Safety Switch -- "Dimple" in Lieu of "Hole"
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Can that dimple be drilled out to allow the use of a padlock, while in the "ON" position, especially in a supervised public location like a baseball stadium?

Does anyone know about any legal case that might cover this situation?

[This message has been edited by Joe Tedesco (edited 04-23-2002).]
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#80504 - 04/23/02 02:49 PM Re: Safety Switch -- "Dimple" in Lieu of "Hole"
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Where opening of a disconnect would create a hazard, I don’t think you could omit the lock. For example, if the switch served lighting indoors or outdoors, operating the switch at night could create a hazard. An open disconnect for a storm-water pump could create a flooding hazard, and may not be evident until an area becomes ‘submersed.’ There are a number of situations where preventing a switch from being operated (opened or closed) at the wrong time could be considered “practical safeguarding of persons and property.”

But then, I wonder if any switch manufacturer provides printed instructions on proper “use” of the dimple?

Top
#80505 - 04/24/02 06:14 AM Re: Safety Switch -- "Dimple" in Lieu of "Hole"
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA

DIMPLE


No Dimple

Which one is permitted?
_________________________
Joe Tedesco, NEC Consultant

Top