The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 262 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80485 - 04/19/02 08:13 PM wire size??
daniel damon Offline

Registered: 01/02/02
Posts: 32
Loc: Ambler,PA, USA
where in the 2002 code book can i find my ans. we need to put in five 200 amp services on a commercial building. five stores (strip). what size does the feeder need to be? itis coming off a tranformer next to the building. no markings on the transformer. i think they should be five 100 amp panels. the store is not that big, 25'x 60'. also can the feeders run along the side of the building, close to the top. my co-worker says yes. then we would tap off of 5 times. need help, thanks guys.


2014 / 2011 NEC & Related Books and Study Guides
#80486 - 04/19/02 09:29 PM Re: wire size??
The Watt Doctor Offline

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
In my opinion, you need to know what the load on each tent space is going to be.
Are they continuous, noncontiuous, motor loads, how much lighting, and what type, etc, etc, etc?
As it looks right now, you are about to build a 1000 amp service for a building that may not need half of that.
Try Parts I & II of article 220.

The Watt Doctor
Altura Cogen
Channelview, TX

#80487 - 04/20/02 05:12 AM Re: wire size??
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA

Are you running feeders or are these service entrances? If this is not a service entrance, you'll need over current protection close to the transformer to protect the feeder.

Like Doc said, do the calculations, SWAGS aren't allowed in this case.

Few things are harder to put up with than the annoyance of a good example.

#80488 - 04/20/02 08:28 AM Re: wire size??
golf junkie Offline

Registered: 04/22/01
Posts: 511
Loc: York, NE
"Try Parts I & II of article 220.

REGARDS!! Come on Doc, what's up with regards? Your fans have high expectations when we see your can't let us down with a simple regards.


#80489 - 04/20/02 07:39 PM Re: wire size??
daniel damon Offline

Registered: 01/02/02
Posts: 32
Loc: Ambler,PA, USA
the owner of the place wanted 200 amp for each store. my boss told him he may not need that. he said that is what he wanted. i agree with what you are saying doc. tom these are service entrance, i think. the are coming from the tranformer. would that be feeders then? hey thanks for the help guys. also, is it ok to run the cables from the tranformer along the building, then tap off for each service?