The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 202 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80482 - 04/19/02 11:36 AM Conduit ?
jbeum Offline
Junior Member

Registered: 04/19/02
Posts: 1
Loc: Ohio
I just finished building a barn that will have a 100a sub panel, I put in a 2" pvc to run 4 THHN cables #3?. Can I put 4 #1/0 copper in a 2" instead? I found a great deal on 1/0 and thought that if I ever put in a bigger panel I would be set. Thanks for any help.

Top
2014 / 2011 NEC & Related Books and Study Guides
#80483 - 04/19/02 11:50 AM Re: Conduit ?
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Yes, no problem.

GJ

Check the lug size in your 100A panel to make sure that it will take the 1/0.

[This message has been edited by golf junkie (edited 04-19-2002).]

Top
#80484 - 04/19/02 04:44 PM Re: Conduit ?
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
jbeum;
Table C-10, pg 70-662, 2002, make sure it's tri-rated....