The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80478 - 04/17/02 02:14 PM Old panel question
Nairb Offline
Junior Member

Registered: 04/17/02
Posts: 3
Loc: Newark, NJ USA
I am changing the breakers in an old GE residential panel that holds TQL breakers.Currently THQL breakers are used to replace these. They snap in place just fine but the hole in the panel cover do not line up just right. My question is, if I trim the extra quarter inch off of the holes to accommodate the breakers will the panel pass inspection? There will be no gap that would allow anything into the interior of the panel.
Thanks for the help
Brian

Top
2014 / 2011 NEC & Related Books and Study Guides
#80479 - 04/17/02 02:50 PM Re: Old panel question
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
NO, I would cite 90.7 in the 2002 NEC --- No alterations can be accepted under any situation or condition. See 110.2
_________________________
Joe Tedesco, NEC Consultant

Top
#80480 - 04/17/02 03:16 PM Re: Old panel question
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I'd chime in with an old favorite in conjunction with 110.2 & that is 110.3(B).

If THQL breakers don't appear in the listing or, more likely, on one of the labels in the breaker box that states which breakers can be used, then you shouldn't use them, even if they do plug on without any trouble.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#80481 - 04/17/02 03:21 PM Re: Old panel question
Nairb Offline
Junior Member

Registered: 04/17/02
Posts: 3
Loc: Newark, NJ USA
Thanks that's what I wanted to know