The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80465 - 04/17/02 06:44 AM 230.50
frodo Offline
Member

Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
i was interested to know what your interpretation is on article 230.50?

does this mean that you can NOT use a SE Cable without a main at the meterbase unless the cable is protected by a raceway?

does SE Cable need a raceway if the MAIN is located inside the building?

thanks for any replies?

-regards

frodo

[This message has been edited by frodo (edited 04-17-2002).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#80466 - 04/19/02 05:20 PM Re: 230.50
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
230.50 Protection of Open Conductors and Cables Against Damage — Above Ground.
Service-entrance conductors installed above ground shall be protected against physical damage as specified in 230.50(A) or (B).
(A) Service Cables. Service cables, where subject to physical damage, shall be protected by any of the following:
(1) Rigid metal conduit
(2) Intermediate metal conduit
(3) Schedule 80 rigid nonmetallic conduit
(4) Electrical metallic tubing
(5) Other approved means
(B) Other Than Service Cable. Individual open conductors and cables other than service cables shall not be installed within 3.0 m (10 ft) of grade level or where exposed to physical damage.
Exception: Type MI and Type MC cable shall be permitted within 3.0 m (10 ft) of grade level where not exposed to physical damage or where protected in accordance with 300.5(D).
 Quote:

does this mean that you can NOT use a SE Cable without a main at the meterbase unless the cable is protected by a raceway?

frodo.....
I would say this would fall under the 'physical damage' interpetation
 Quote:

does SE Cable need a raceway if the MAIN is located inside the building?

this is pertinent also to damage, and as such may be viewed regardless of the mains location...allthough an OCPD would probably cut some slack in this respect.....

so we are left with hypotheticals...
why not?

>>>>A simple service, SEU drop to 100a meter, SEU out the bottom of said meter runs down, along a residence at 2-3'from grade, and into the sill 40' away.

all fine & well......

The occupant then constructs a ( pick a problem of your choice) kennel for hybird attack wolfs along said wall.....

Top
#80467 - 04/19/02 06:14 PM Re: 230.50
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
The kicker here is that everyone seems to differ on the "subject to physical damage" point. I know it varies from town to town here. Generaly I stick with pvc and that works out well.

Top
#80468 - 04/20/02 07:53 PM Re: 230.50
frodo Offline
Member

Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
thanks for the replies. i asked the question because my local jurisdiction requested that the sec i installed be in a raceway. i asked the ahj which article it was that required the raceway...not trying to call them on it but to be in the know if it was not allowed, i hadnt heard...initially one of the inspectors had thought it may be 230.50 but he did not say that that was the article he said that he had not looked it up yet..

i had done this before with no problem so i was kinda unaware that it was not allowed here. i was curious as to whether this was something new in 2002.

i finally spoke to the ahj and they said that it was their intent to provide more protection on a SEC since the only protection was at the pole..i usually use pvc myself as well but in this case i wanted to use the sec. it was a old house that had some unconventional framing..

i am planning to install aluminum flex there to provide the raceway. it would be difficult to install pvc now everything is done as far as the rough-in..

i plan to use 3 #2 copper thhn and 1" aluminum flex and a bonding bushing at the meterbase. that should do it...?

the ahj here says they will only allow SEC cable between the meterbase and the loadcenter if their is a main at the meterbase..i agree with this and will use a ocpd at the meter. ..i dont need a main inside then do I? as i understand it...the main shall be located either outside or immediately inside..?

the ahj here says they only allow 10' of use inside the building..i think that is in the code though..

thanks for the info

-regards

frodo

[This message has been edited by frodo (edited 04-21-2002).]