The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 162 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80427 - 04/11/02 09:59 AM Derating and Maximum # of Conductors
Admin Online   content

Administrator
Member

Registered: 10/07/00
Posts: 3187
Loc: NY, USA
Quote:
Would you help us resolve a question of derating and maximum number of conductors in a raceway?

Please refer to the 2002 NEC Handbook for the following question:

We are discussing how to properly derate conductors in raceway when the quantity of conductors exceeds 85.

The wiring application in question is for theaters and involves stage, concert and house lighting circuits controlled by solid state dimming racks. Many dimming racks in large theaters have 90 or more dimmer modules resulting in at least 180 current carrying conductors plus ground conductors. Metal wireway is often used to route conductors from the dimmer racks to the fixtures. The wireway is sized for the maximum 20 percent fill required by Article 376. We are applying Article 520.6 that grants exception to the 30 conductor maximum rule in Article 376.

The question of properly derating remains. Note: Load diversity is often 50% or greater.

Table B.310.11 appears to apply. The problem is that this table does not seem to address more than 85 conductors. The FPN following the table refers to "special calculations required" but does not specify further reading or guidelines to perform the calculations.

Jeffrey M. Leavenworth, P.E.

Top
2017 / 2014 NEC & Related Books and Study Guides
#80428 - 04/11/02 08:53 PM Re: Derating and Maximum # of Conductors
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
My NEC [1999] is in the Van and it's getting late, but I would like to address this message, so I'll toss some numbers and stuff in this thread later.

Scott SET
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#80429 - 04/13/02 10:39 AM Re: Derating and Maximum # of Conductors
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Jeff,
I do not have the 2002 code yet but the
99 code section 318-11 seems to apply to your installation.

Top
#80430 - 04/15/02 10:28 AM Re: Derating and Maximum # of Conductors
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
This query has been lying here festering for a couple of days. Seems like no one really wants to get out in the lead (and become a target).

Here goes. If you are applying 520.6, and are otherwise in compliance with that article, no derating of the conductors is required.

The last sentence waives the 30 conductor limitation of 366.6 & 376.22 Both of these require derating when exceeding 30 current carrying conductors. Since the rule is waived, derating is not required.

Do I need to put on my asbestos coveralls?

[This message has been edited by Tom (edited 04-15-2002).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals