#80408 - 04/09/02 11:13 PM Service-Entrance Conductors  
MVillines  Offline
Member
Joined: Jan 2002
Posts: 21
Henderson
Can the grounded conductor at the service head (service point) be identified by stripping the insulation off the conductor as described in section 250.114 or must it be identified per section 200.6? Article 230 seems to be silent except for section 230.41, which permits the grounded conductor to be bare.


2017 / 2014 NEC & Related Books and Study Guides

#80409 - 04/10/02 12:59 PM Re: Service-Entrance Conductors  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
No, Article 250 applies to grounding conductors, not grounded conductors. The grounded conductor must be identifed per Article 200.
Don(resqcapt19)


Don(resqcapt19)

#80410 - 04/10/02 10:58 PM Re: Service-Entrance Conductors  
MVillines  Offline
Member
Joined: Jan 2002
Posts: 21
Henderson
Don
If you identify the grounded service-conductor per Article 200, that would mean you would have to mark the bare grounded conductor with paint or tape if the conductor is larger than 6 AWG. If the conductor is #6 AWG or smaller the identification would have to continuous the entire length of the conductor. This would conflict with section 230.41 that permits the conductor to be bare. What would an electrician say about the inspector that required white tape or paint on the bare conductor?


#80411 - 04/11/02 07:58 AM Re: Service-Entrance Conductors  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
local poco requires grounded conductor to be stripped 6" from weatherhead. Will not accept tape or paint- call those methods not permenant.
Different local rules in other poco areas do apply.


ed

#80412 - 04/11/02 10:58 AM Re: Service-Entrance Conductors  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
MVillines,
The original question asked about striping the end of an insulated conductor to identify it as a grounded conductor. While 230.41 does permit the use of a bare conductor as a grounded conductor, it does not permit you to strip the end of an insulated conductor to identify it as the grounded conductor. If the grounded conductor is an insulated conductor the code requires identification per Article 200. Article 200 does not require additional identification of a bare grounded conductor.
Don(resqcapt19)


Don(resqcapt19)


Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7657 MB (Peak: 0.9039 MB) Zlib enabled. Server Time: 2017-03-25 17:33:41 UTC