The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80403 - 04/09/02 05:01 PM Required Circuits
frodo Offline
Member

Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
as far as i can tell only one circuit is required in the living room? for some reason i am thinking there was a rule that required two for the kitchen and two for the living room...

any replies would be appreciated..

thanks
frodo

Top
2014 / 2011 NEC & Related Books and Study Guides
#80404 - 04/09/02 06:18 PM Re: Required Circuits
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
The only place 2 are required is the kitchen small appliance circuits. Other than one for the laundry and one for the bathrooms, I believe you could conceivably be code-compliant with just one for the whole rest of the house, if it was small enough.

[This message has been edited by Redsy (edited 04-09-2002).]

Top
#80405 - 04/09/02 09:11 PM Re: Required Circuits
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Frodo,
210-52 can be a bit confusing. Specifically the two small appliance circuits are required to be distributed among the Kitchen, Pantry, Breakfast room, dining room, OR SIMILAR AREA.
210-52 (b)(1) 99 code.

It is not a hard thing for me to believe that somewhere in the country some inspection agency has determined that a living room is similar, but let's look at the intent of that section.

It was written because people are likely to plug in high draw appliances in those rooms, coffee pots, toasters, broilers, etc.. Not likely to happen in a living room

The living room (referenced in 210-52(a)) is occasionally confused in this manner, but it only has to have its receptacles on the General Purpose outlets, no reference to number of circuits.

Top
#80406 - 04/10/02 05:00 AM Re: Required Circuits
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Not to stir things up here, but who the @%&* would confuse a living room with a kitchen? If I come across this guy and he is doing inspections I'm calling the cuckoo farm!

Top
#80407 - 04/10/02 08:57 AM Re: Required Circuits
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Some inspectors have trouble with single room apartments.