ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,894 Are you busy
166,769 Re: Forum
160,885 Need opinion
Who's Online Now
0 registered members (), 98 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#80403 - 04/09/02 08:01 PM Required Circuits  
frodo  Offline
Member
Joined: May 2001
Posts: 129
louisville, ky usa
hi,
as far as i can tell only one circuit is required in the living room? for some reason i am thinking there was a rule that required two for the kitchen and two for the living room...

any replies would be appreciated..

thanks
frodo


2017 / 2014 NEC & Related Books and Study Guides

#80404 - 04/09/02 09:18 PM Re: Required Circuits  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
The only place 2 are required is the kitchen small appliance circuits. Other than one for the laundry and one for the bathrooms, I believe you could conceivably be code-compliant with just one for the whole rest of the house, if it was small enough.

[This message has been edited by Redsy (edited 04-09-2002).]


#80405 - 04/10/02 12:11 AM Re: Required Circuits  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
Frodo,
210-52 can be a bit confusing. Specifically the two small appliance circuits are required to be distributed among the Kitchen, Pantry, Breakfast room, dining room, OR SIMILAR AREA.
210-52 (b)(1) 99 code.

It is not a hard thing for me to believe that somewhere in the country some inspection agency has determined that a living room is similar, but let's look at the intent of that section.

It was written because people are likely to plug in high draw appliances in those rooms, coffee pots, toasters, broilers, etc.. Not likely to happen in a living room

The living room (referenced in 210-52(a)) is occasionally confused in this manner, but it only has to have its receptacles on the General Purpose outlets, no reference to number of circuits.


#80406 - 04/10/02 08:00 AM Re: Required Circuits  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Not to stir things up here, but who the @%&* would confuse a living room with a kitchen? If I come across this guy and he is doing inspections I'm calling the cuckoo farm!


#80407 - 04/10/02 11:57 AM Re: Required Circuits  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Some inspectors have trouble with single room apartments.


Ron


Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7657 MB (Peak: 0.9014 MB) Zlib enabled. Server Time: 2017-03-30 20:18:51 UTC