The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 164 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80401 - 04/09/02 08:30 AM sub panel to storage building/shop
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
In wiring a storage building from home panel I`m running 100 amp service to it 4 wire use now I`m not sure do I drive a ground rod or 2 ground rods or does the 4th egc wire take care of it. Thanks in advance

Top
2017 / 2014 NEC & Related Books and Study Guides
#80402 - 04/09/02 01:44 PM Re: sub panel to storage building/shop
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Reel,
99 code 250-32. If your building has more than one ckt (and I'm pretty sure we can assume it does) you have to have a grounding electrode (rod, water pipe, effectively grounded bldg steel, etc.) connected to your green, bare, whatever grounding conductor.

Using 4 conductors, your neutral and ground are kept separate at the out-building service, but the ground must have an electrode.