#80401 - 04/09/02 08:30 AM sub panel to storage building/shop
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 178
Loc: nc
In wiring a storage building from home panel I`m running 100 amp service to it 4 wire use now I`m not sure do I drive a ground rod or 2 ground rods or does the 4th egc wire take care of it. Thanks in advance
Top
2017 / 2014 NEC & Related Books and Study Guides
#80402 - 04/09/02 01:44 PM Re: sub panel to storage building/shop
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Reel,
99 code 250-32. If your building has more than one ckt (and I'm pretty sure we can assume it does) you have to have a grounding electrode (rod, water pipe, effectively grounded bldg steel, etc.) connected to your green, bare, whatever grounding conductor.

Using 4 conductors, your neutral and ground are kept separate at the out-building service, but the ground must have an electrode.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals