The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Parking lot pole light swap....
by HotLine1
10/23/16 09:39 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80401 - 04/09/02 08:30 AM sub panel to storage building/shop
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
In wiring a storage building from home panel I`m running 100 amp service to it 4 wire use now I`m not sure do I drive a ground rod or 2 ground rods or does the 4th egc wire take care of it. Thanks in advance

2014 / 2011 NEC & Related Books and Study Guides
#80402 - 04/09/02 01:44 PM Re: sub panel to storage building/shop
George Corron Offline

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
99 code 250-32. If your building has more than one ckt (and I'm pretty sure we can assume it does) you have to have a grounding electrode (rod, water pipe, effectively grounded bldg steel, etc.) connected to your green, bare, whatever grounding conductor.

Using 4 conductors, your neutral and ground are kept separate at the out-building service, but the ground must have an electrode.