The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 114 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80365 - 04/03/02 07:17 PM service disconnects
kenrod3020 Offline

Registered: 02/27/02
Posts: 15
Loc: ashland ky. us
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?

2014 / 2011 NEC & Related Books and Study Guides
#80366 - 04/04/02 04:41 AM Re: service disconnects
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]

#80367 - 04/13/02 09:32 AM Re: service disconnects
tdhorne Offline

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison