The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80365 - 04/03/02 07:17 PM service disconnects
kenrod3020 Offline
Member

Registered: 02/27/02
Posts: 15
Loc: ashland ky. us
200 amp service, in a strip mall,200 amp disconnect at meter base. service panel about 100 ft. away is there a code requiring a main breaker in the service panel? and if not would you do ?
_________________________
kenrod3020

Top
2014 / 2011 NEC & Related Books and Study Guides
#80366 - 04/04/02 04:41 AM Re: service disconnects
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
There's not a requirement for an additional disconnecting means at the subpanel.
As long as the main breaker at the meter base is accessible to the occupant per 240.24(B), and 230.72(C) I would just use a main-lug-only subpanel.
If it's one of those places that (in violation) keeps an electrical room locked from the occupants, I'd probably add the main.

[This message has been edited by electure (edited 04-06-2002).]

Top
#80367 - 04/13/02 09:32 AM Re: service disconnects
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
How would supplying a main breaker in the panel address the requirement in 225.35 for occupant access to the supply disconnecting means?
--
Tom

225.35 Access to Occupants.
In a multiple-occupancy building, each occupant shall have access to the occupant?s supply disconnecting means.
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top