#8035 - 03/05/02 02:18 PM Grounding Check on Building
Chris Paul Offline
Junior Member
Registered: 03/05/02
Posts: 6
Loc: Owenton
I've been coming to this site for awhile now and have got some good information here. That is why I come to you all with this question. I work in a factory which getting ready to partake in the OSHAS 18001 safety program. I don't know if anyone is familiar with this or not, but as the electrician and maintenance guy on sight I was asked to check the grounding system of the building. I'm not really sure what kind of checking they want me to do, but I thought maybe someone here has done this sort of thing before and could give me a heads up on maybe what they want and how to do this. I called the AHJ for this area and he didn't really know of anything to tell me. Thanks for your help.
Top
Work Gear for Electricians and the Trades
#8036 - 03/06/02 09:53 AM Re: Grounding Check on Building
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
Rent a Biddle Ground Tester from a rental place that has such equipment. Read the instructions and do as they recommend. Have a set of your building drawings available so you will know where the ground test wells are located.
Good luck.
Top
#8037 - 03/06/02 09:35 PM Re: Grounding Check on Building
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
Start by finding out what OSHA 18001 standards call for. If grounding is your only concern, I would find a book that will guide you through the NEC, and give you a better understanding of system grounding, circuit grounding, equipment grounding, performance of fault current path, etc., etc., etc.
Whatever 18001 calls for, find as much information about those subjects, and break your facility down into systems, or sections, and systematically work them all until you meet 18001 requirements.
Also, take 2 asprins, and call me in the morning.
Regards,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals