The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
39 minutes 26 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 234 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80345 - 03/31/02 08:59 AM Location of sub-panel
Mike Wescoatt Offline
Member

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
I'm helping a friend build a new second floor laundry room and have run cable for a 40A sub-panel for the washer, dryer, outlets and lights. This room is in an old attic space where the ceiling runs from 9' to 5' over the length of the room. In the short end of the room (ceiling from 4.5' to 2') they are building a storage space (insulated and rough drywalled) accessed by a 36Hx24W" door. Do you see any problems or restrictions with placing the panel just inside the small door? The center of the panel would be at 36" and there will be permanent lighting in this 60"x96" crawlspace.
I would put it in the new room, but all of the walls have washer, dryer, or cabinets on them...
_________________________
Mike Wescoatt

Top
2014 / 2011 NEC & Related Books and Study Guides
#80346 - 03/31/02 01:21 PM Re: Location of sub-panel
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
There might be a lack of working clearance. The depth of the working space is 36" from the cover of the panel & the space is 30" wide. Can you clarify what the dimensions of this storage room are & include the depth?

Another problem is that you've told us this is a storage area. 110.26(B) says the working space is not to be used for storage.

Since this is a residential installation, the headroom requirement is waived. Exception to 110.26(E)


[This message has been edited by Tom (edited 03-31-2002).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#80347 - 03/31/02 04:15 PM Re: Location of sub-panel
Mike Wescoatt Offline
Member

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
Panel is located on South wall just inside door which is on West wall. E/W dimension is 60", N/S dimension is 96". There would be no storage space in front of the panel since anything stored here would be in the way of the access to the space, but the depth of the space could be limited to the width of the door, 24". Could this be remedied by permanently marking on the floor "KEEP THIS AREA CLEAR"?
_________________________
Mike Wescoatt

Top
#80348 - 04/01/02 04:53 AM Re: Location of sub-panel
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
There appears to be adequate working space.

Signs are about useless (opinion) since the panel is close to the door, chances are that there wouldn't be anything piled up in front of the panel.

The only other potential problem would be 110.26(C)(1), access to working space is not defined in this particular case & would be a judgement call on the part of the AHJ. I've seen emergency escape doors this size at some coal mine installations (aboveground). State & federal mine inspectors are even tougher than the inspectors we deal with so I'd be inclined to say that the access is adequate.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.