does a dish washer require a seperate circuit or not ?
Top
2017 / 2014 NEC & Related Books and Study Guides
#80250 - 03/22/02 01:26 PM Re: dish washer
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Well, it depends on how much of a load the dishwasher is. Start at 422-10(b) which refers to 210-23 if the circuit will supply the dishwasher and other loads.

If the dishwasher is cord & plug connected & is portable, it cannot exceed 80% of the circuit rating.

If the dishwasher is fastened in place, it cannot exceed 50% of the circuit rating if the circuit also supplies any of the other loads mentioned in 210-23(a).
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#80251 - 03/22/02 01:40 PM Re: dish washer
motor-T Offline
Member
Registered: 11/10/01
Posts: 280
Loc: Girard, Ohio, USA
That is as long as it is not put on the small appliance circuit, ala

210.52(B)2 No other outlets. The two or more small appliance branch circuits specified in 210.52(B)1 shall have no other outlets.

So I would say yes it needs its own circuit.
-Mark-
Top
#80252 - 03/22/02 04:54 PM Re: dish washer
George Offline
Member
Registered: 02/23/02
Posts: 375
Different codes have different requirements.

From the 1998 ICC 1 & 2 Family dwelling Code, it is clear that the recept for the dishwasher may be on the small appliance circuits:

"Other receptical outlets provided ... shall be supplied by the small appliance branch circuits or other branch circuits."

I prefer to place the dishwasher, refrigerator, and disposal on one dedicated circuit. That might be an option for you.
Top
#80253 - 03/22/02 05:31 PM Re: dish washer
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
My preference is simply to overwire. This is NOT a bidwinner, only condusive to a good nights sleep...
All my kitchens have seperate appliance circuits
( which is why i need a 40 cir MLO {200A} panels in 100A calc'ed homes...)
WHY?
because the majority of old work problems is lack of ampacity....
Top
#80254 - 03/23/02 07:22 PM Re: dish washer
eman1963 Offline
Member
Registered: 01/24/02
Posts: 22
Loc: rhode island
i think the frig dishwasher and disposal would be to much on one circuit.
i usually run one circuit to each
Top
#80255 - 03/24/02 04:45 AM Re: dish washer
motor-T Offline
Member
Registered: 11/10/01
Posts: 280
Loc: Girard, Ohio, USA
eman
The refrigerator is allowed to be on the samll appliance branch circuit, or not your choice.
The Dishwasher and disposer are not allowed to be on the small appliance circuits.
They must be on their own circuits.
-Mark-
Top
#80256 - 03/24/02 04:48 PM Re: dish washer
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
A sepater ckt. for a GD seems overkill.
I like a 20 amp ckt. for GD & DW.
Dedicated 15 amp for frig.
Top
#80257 - 03/24/02 04:49 PM Re: dish washer
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
A sepater ckt. for a GD seems overkill.
I like a 20 amp ckt. for GD & DW.
Dedicated 15 amp for frig.
I'm more concerned with hte defrost cycle of the frig. than the running cycle. Anyone got the numbers?
Top
#80258 - 03/24/02 05:29 PM Re: dish washer
NonLinearLoad Offline
Member
Registered: 03/23/02
Posts: 53
Loc: McHenry, IL. USA
I'm in agreement with the majority.
I give dish/disp it's own cicuit. Frig. is always on its own. Micro/stove electronic ignition, on its own, too many inspectors have insisted on this one, micros are too big and bad nowadays.
Two small appliance as per code, yet I try not to exceed 3 outlets or 4 on each one.
And all of this depends on the homeowner with their specific appliances in mind, let's get toaster oven and a countertop micro going together, oh a little coffee, and some toast too, and they are all on the same wall.
Overwiring up front can avoid the service calls. Everything seems to get bigger and badder.
Everything is networked and typically numerous 1/2" HRS, 3/4" if the wire is dumped ASAP.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals