#80219 - 03/18/02 07:38 AM 50 amp hot tub
JMichael Offline
Member
Registered: 03/10/02
Posts: 60
Loc: Norwich, NY, USA
Someone told me that a 50 amp. hot tub does not have to be GFI protected. Just bonded with a #6 bond wire to the panel. (Also with a disconnect.) He claims that only 15 and 20 amp. circuits require gfi protection. Being I am not as indebth to the NEC as most of you. Could someone please tell me if the advice I am given is true..

James
Top
2017 / 2014 NEC & Related Books and Study Guides
#80220 - 03/18/02 09:27 AM Re: 50 amp hot tub
therain4 Offline
Member
Registered: 12/18/00
Posts: 38
Loc: Dunmore,Pa. U>S.A.
James Article 680.22 A (5) (2002 NEC)
"Receptacles that supply pool pump motors and that are rated 15 or 20 amperes, 120 volt through 240 volts, single phase, shall be provided with GFCI protection." It is section II permenatly installed pools but both section 680.42 and 680.43 reference compliance to section I and II.
Top
#80221 - 03/18/02 12:34 PM Re: 50 amp hot tub
JMichael Offline
Member
Registered: 03/10/02
Posts: 60
Loc: Norwich, NY, USA
There is no recep. its 50 amp. hard wired to the unit. This is whats puzzling me.
Top
#80222 - 03/18/02 12:36 PM Re: 50 amp hot tub
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
I don't think a hot tub is required by the NEC to have GFCI protection if it is hard wired. If it is cord and plug connected, 680.43(A)(4) will require GFCI protection. The listing instructions may also require GFCI protection.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#80223 - 03/18/02 01:17 PM Re: 50 amp hot tub
motor-T Offline
Member
Registered: 11/10/01
Posts: 280
Loc: Girard, Ohio, USA
Every Hot-tub and Spa I have seen says in the instructions if hard wired use a 50 GFCI breaker, a lot of the units that can run on 120 volts have a gfci built right into the cord.
I wouldn't want to put one in without it being GFCI protected.

_Mark
Top
#80224 - 03/18/02 01:39 PM Re: 50 amp hot tub
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
This gets a little clearer (I think) in the 2002 code. 680.4 requires compliance with parts I & IV of the article, part IV is the section that deals with hot tubs & spas.

680.42 has some additional wiring requirements for outdoor installations.

680.44 requires GFCI protection. Of course, theres the usual cast of exceptions.

Every hard wired tub I've seen has GFCI protection mandated in the instructions.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#80225 - 03/18/02 03:49 PM Re: 50 amp hot tub
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Im not sure of the brand but there is a 50 amp disconnect with built in gfi protection made for hot tubs. I see it at my supply house every day, let me know if you want more info.
Top
#80226 - 03/18/02 05:22 PM Re: 50 amp hot tub
motor-T Offline
Member
Registered: 11/10/01
Posts: 280
Loc: Girard, Ohio, USA
In the code Handbook under 680.44, It says, "The requirements of 680.44 specify that field-assembled Spas and Hot tubs with heater loads of 50 amps or less are to be GFCI protected"
I cannot imagine putting one of these units in without GFCI protection, Lloyds of London wouldnt have that kind of money for the insurances and the lawsuits.
-Mark
Top
#80227 - 03/18/02 07:36 PM Re: 50 amp hot tub
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
motor,
You are correct, 680.44 does require GFCI protection for the hot tub outlet. I missed that.
don
_________________________
Don(resqcapt19)
Top
#80228 - 03/18/02 10:17 PM Re: 50 amp hot tub
JMichael Offline
Member
Registered: 03/10/02
Posts: 60
Loc: Norwich, NY, USA
That is what I thought.. Just have to becareful who you take advice from.. I mean to say many of the older homes here on long island are run on a 60 amp service. So lets take that service and feed a hot tub! It would be stupid not to GFI protect it..

James
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals