#80186 - 03/14/02 10:09 AM # of Ground rods
AndrusT Offline
Member
Registered: 03/14/02
Posts: 24
Whats the rule, on when you need to have 2 ground rods?
I have heard 2 reasons.
1. When the service is over 200 amps.
2. When your water pipe has a plastic main.

I have also heard the reason for this is cause you need 10 feet of ground (rod, or copper main) going into the earth. I can't seem to find this stuff myself. Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#80187 - 03/14/02 01:06 PM Re: # of Ground rods
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Unless you've got the $$$ for the tester & time to waste, you'll need 2 rods at all times.

See 250-56 1999 NEC
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#80188 - 03/14/02 01:54 PM Re: # of Ground rods
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2342
Loc: West Virginia
2002 NEC 250.56

A little more explanation:

Unless you have the equipment and time to prove that your one grounding electrode has a resistance of 25 Ohms or less (and the Power Company doesn't mind only one) then the NEC requires no less than two.

Ground Meggers are expensive...

Also, 250.52(A)(5) requires 8 ft to be in contact with the earth. 10 ft. could be your local PoCo requirement.

[This message has been edited by sparky66wv (edited 03-14-2002).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#80189 - 03/14/02 04:34 PM Re: # of Ground rods
motor-T Offline
Member
Registered: 11/10/01
Posts: 293
Loc: Girard, Ohio, USA
AndrusT:
As it was explained to me by our inspector, he said, " Show me 25 ohms to ground, or drive two ground rods, its that simple."
-Mark-
Top
#80190 - 03/14/02 07:09 PM Re: # of Ground rods
spkjpr Offline
Member
Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Motor t, my inspector is even easier than that. He just says two ground rods no matter what.
Top
#80191 - 03/22/02 02:48 AM Re: # of Ground rods
joeh20 Offline
Member
Registered: 03/21/02
Posts: 95
Loc: Tullahoma, TN, 37388
Our local PoCo went behind their own office and drove 10 8' ground rods and never got 25 ohms. So they let us get by with two now. I worked on a 1200 amp 480v with 5 rods 10' apart cadwelded to 4/0 copper in addition to a clamp on a 4" galvanize water line thirty feet in direct contact with the earth and never got 25 ohms. But the key here was undisturbed earth, seems any fill really messes thing up.
_________________________
Lighting the way
Top
#80192 - 03/24/02 05:57 PM Re: # of Ground rods
NonLinearLoad Offline
Member
Registered: 03/23/02
Posts: 56
Loc: McHenry, IL. USA
Illinois.
One rod as supplemental to primary ground as in city supplied water, attachment per code distances, service size to AWG sizing.
Got a well, TWO rods 6' apart all continous wire. Still it gets attached to the first copper accessible to tank as the backup water in the hole deal, got water it gets to the earth.
Wisconsin... TWO rods, due to soil.
Top
#80193 - 04/02/02 03:56 PM Re: # of Ground rods
electricdiver Offline
Junior Member
Registered: 04/02/02
Posts: 2
Loc: howell,nj,usa
read 250-81 carefully. you don't need any grd rods if you meet the first several conditions
Top
#80194 - 04/02/02 05:25 PM Re: # of Ground rods
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
All you really have to do is have less than 25 ohms to ground on your grounding electrode connection...if it takes 1 rod, or 100.
(rods are kind of a junky ground path. If you're in trouble, you can pour a concrete encased electrode aka:Ufer, by just putting 20' of GEC sized Cu wire in a trench filled with concrete. Unless you have some kind of "resistance dirt", it'll pass)
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals