#80156 - 03/06/02 05:17 PM Motor Control Centers  
tmon  Offline
Member
Joined: Jul 2001
Posts: 29
Does anyone have any information concerning adding onto a motor control center by connecting cables to the horizontal main bus? A breaker would be installed at the end of the MCC and it would be within 10'. I am actually hoping to find arguments against doing it. Thanks


2017 / 2014 NEC & Related Books and Study Guides

#80157 - 03/06/02 06:43 PM Re: Motor Control Centers  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
I would begin by reading the 2002 NEC Part VIII. Motor Control Centers in Article 430.
tmon:

I can think of a few items that would lead me to believe that what you propose may be in violation of the rules in some parts of this place in the code, and in addition, 90.7 and maybe even 110.2 to give a few references for others to think about when responding to your question.


Joe Tedesco, NEC Consultant

#80158 - 03/06/02 07:32 PM Re: Motor Control Centers  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Does the cable ampacity equal or exceed that of the main bus? Are there provisions to terminate cables in the MCC or you making some makeshift connection?
Don(resqcapt19)


Don(resqcapt19)

#80159 - 03/06/02 08:02 PM Re: Motor Control Centers  
tmon  Offline
Member
Joined: Jul 2001
Posts: 29
The cable would not be equal to the bus amperage. I could not find anything in the NEC stating that the tap conductors be equal to or exceed the conductors that are being tapped. The connections would be with mechanical lugs.


#80160 - 03/06/02 10:13 PM Re: Motor Control Centers  
wirewiz  Offline
Member
Joined: Jan 2002
Posts: 122
WA.
Sounds to me like you are adding a breaker because the MCC is tapped out. Are there provisions on the bus and literature from the manufacturer that will allow a connection to the bus? My understanding has always been that as soon as you start modifying equipment (in a way that it was not designed for) in the field you void the UL listing.
Depending on the buss rating and the actual load on the MCC you may get the manufacturer to allow this and re-certify the panel. Another way I have done this in the past is to install a "Top Hat" on the Mcc. (which is similar to a section of bus duct) that will allow you to attach an additional Mcc section next to or in the general vicinity of the existing Mcc. Make sure this is engineered, approved by the AHJ and who ever builds it can back it up with a UL listing.
Before you start. There are a few panel shops out there that can do this you just have to search. Depending on the size of your Mcc, length of new feeders etc. this can be a lower cost alternative than replacing the existing one.


#80161 - 03/07/02 08:22 AM Re: Motor Control Centers  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
What is the purpose of the extension.
Can you provide more detail?



Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.002s) Memory: 0.7743 MB (Peak: 0.9200 MB) Zlib enabled. Server Time: 2017-03-23 02:17:34 UTC