The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/17/17 09:41 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 19
gfretwell 13
ghost307 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 62 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80152 - 03/06/02 12:13 PM Motion Controlled Switch for panelboard illumination
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Can, and should a motion controlled switch be used to control illumination of panelboards? What are your thoughts?

Bill

Top
2017 / 2014 NEC & Related Books and Study Guides
#80153 - 03/06/02 12:27 PM Re: Motion Controlled Switch for panelboard illumination
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Bill:

I would answer NO, because of the rule in 110.26(D) Illumination last sentence.

Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, or motor control centers installed indoors.

Additional lighting outlets shall not be required where the work space is illuminated by an adjacent light source or as permitted by 210.70(A)(1), Exception No. 1, for switched receptacles.

In electrical equipment rooms, the illumination shall not be controlled by automatic means only.
_________________________
Joe Tedesco, NEC Consultant

Top
#80154 - 03/06/02 03:57 PM Re: Motion Controlled Switch for panelboard illumination
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Joe,

Thanks, I would agree about it probably not being a good idea, but (strictly speaking) I don't see this code section prohibiting it for the following reasons;

What if it is not in a separate room?
Does the term 'Automatic' really include Motion-Controlled?
If it is a Motion-Controlled wall switch it also has a manual setting.

Bill

Top
#80155 - 03/06/02 08:39 PM Re: Motion Controlled Switch for panelboard illumination
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
I was just thinking that maybe I was interpreting the words 'Automatic Means' too literally.

My first thought was that 'Automatic Means' meant something that wastotally under the control of outside forces and that the person in the room had no way of controlling it at all. (This would literally be wrong if the light could be controlled by his movements)