The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#80120 - 02/28/02 07:06 PM Class Two circuits
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Same project as the isolated ground question. The main gear is a panel group. All distribution panels and branch circuit panels are contained in one 30”deep 7’6” wide piece of gear. There is a contactor section in the middle. On this contactor board will be a pilot relay for every contactor. The pilot relays are 24VAC controlled by the EMAC system. These 24VAC control circuits are fed from class 2 power supplies. The wiring will have to chase through the gear to get to the contactor section. I believe this to be a violation of 725.55(A). Again, I was told, “ What’s the problem.” Am I all wet?

Top
2014 / 2011 NEC & Related Books and Study Guides
#80121 - 02/28/02 09:21 PM Re: Class Two circuits
Elzappr Offline
Member

Registered: 12/20/01
Posts: 273
Loc: Oregon
Nah..you're right Nick. This is such a typical case. Is there some way to keep 1/4in separation?

Top
#80122 - 03/01/02 05:11 AM Re: Class Two circuits
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Nick,
I don't know if this is applicable to your case, but check 725.52(A) Exception #2. It seems to modify (read Trash) 725.55.