#79996 - 02/12/02 04:35 PM 2 pole GFCI circuit breaker
tmon Offline
Member
Registered: 07/05/01
Posts: 29
Does a 2 pole gfci circuit breaker compare the two ungrounded conductors ampacities like a single pole compares the hot and neutral? I am wondering if I can use it on a masonry saw that does not utilize a neutral conductor and still be protected. Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#79997 - 02/12/02 05:07 PM Re: 2 pole GFCI circuit breaker
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
It compares the 2 hots if it is a 240 GFCI and compares a three wires if it is a 120/240 GFCI. Either one will provide protection for a 240 volt saw.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top