The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 206 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79900 - 02/03/02 07:26 PM Meter disconnect switches
MVillines Offline
Member

Registered: 01/07/02
Posts: 21
Loc: Henderson
2002 NEC Article 230.82 EX. (2) Permits a meter disconnect switch to be connected on the supply side of the service disconnect. This has never been a practice in western Kentucky but I have read that it is normal in other parts of the country.
Is this for the safety of the utility for changing meters?
Does it always have to be on the supply of the meter or can it be located on the load side?
Can this switch have integral overcurrent Protection?

Top
2014 / 2011 NEC & Related Books and Study Guides
#79901 - 02/03/02 07:48 PM Re: Meter disconnect switches
Tom Baker Offline
Member

Registered: 10/09/01
Posts: 31
Loc: Bremerton WA
Its a required practice in the western us, for services 300V phase to phase and greater. Its for the safety of the meterman, as pulling a 480 v meter under load can be very dangerous. This is a USEC requirement.Also any of our commerical meters have to have manual bypass sockets so the meter can be pulled for testing.

A meter is not required by NEC. Its the utility that wants it installed. I've been installing disconnects ahead of the meter for 20 years. Often I will use a non-fused disconnect.

Top
#79902 - 02/03/02 07:57 PM Re: Meter disconnect switches
MVillines Offline
Member

Registered: 01/07/02
Posts: 21
Loc: Henderson
Tom
Could this disconnect be located on the load side of the meter. Even though the meter would be energized there would be no current flow with the disconnect in the open position. Has anyone installed the disconnect with overcurrent protection?

Top
#79903 - 02/03/02 08:37 PM Re: Meter disconnect switches
NoShorts4Me Offline
Member

Registered: 01/14/02
Posts: 35
Loc: southern california
MV,
Check out SquareD.com
Check out the combo residential panels. These are typical of a residential service here in southern california. The main breaker AFTER the meter is located on the customer "side" of the panel with distribution, but more easily accessible then in the basement. The local utilies here also require a "commercial by-pass" ahead and after the meter for meterman to safely work on the meter. This is accomplished by removable "nuts" that span the busbars.The meterman can also de-energize service this way, with out removing the meter.
You can also have Meter-Main panels with no distribution, with the OC being either breaker or fusible pull out, also with mandatory commercial by-pass. These are typical in 3R commercial applications, especially at 480v.
Hope this sheds some light.
NS4M

[This message has been edited by NoShorts4Me (edited 02-03-2002).]

Top
#79904 - 02/03/02 08:43 PM Re: Meter disconnect switches
NoShorts4Me Offline
Member

Registered: 01/14/02
Posts: 35
Loc: southern california
Tom,
Did you say that you install service disconnects AHEAD of the meter? Are you talking about seperate from the meter socket or panel? ie. service drop, non-fusible disconect, meter, customer?
Maybe I misread your post.
NS4M

Top
#79905 - 02/03/02 09:18 PM Re: Meter disconnect switches
MVillines Offline
Member

Registered: 01/07/02
Posts: 21
Loc: Henderson
NoS..
I understand the type of panel you refered too. My point is by installing this equipment using section 230.82 (2), the conductors leaving this panel would be considered “service conductors” not feeder conductors.
If this equipment were installed on a pole remote form the building being served; how would this relate to section 230.7 Other Conductors in Raceway or Cable? Using 230.82 (2) theoretically the service conductors down the pole to the meter and (not service) disconnect could occupy the same conduit as the service conductors going back up the pole that could serve a building with the service equipment.

Top
#79906 - 02/03/02 09:24 PM Re: Meter disconnect switches
MVillines Offline
Member

Registered: 01/07/02
Posts: 21
Loc: Henderson
Could someone please post the link to the web site announcing the production of the Romex brand NM Cable in colors by size of conductor?
Thanks

Top
#79907 - 02/04/02 06:43 AM Re: Meter disconnect switches
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
MV,

Look here for the Colored NM Cable;
http://www.southwire.com/

Previous Discussion on it here was;
http://electrical-contractor.net/ubb/Forum1/HTML/000840.html

Bill

Top
#79908 - 02/06/02 07:04 PM Re: Meter disconnect switches
Tom Baker Offline
Member

Registered: 10/09/01
Posts: 31
Loc: Bremerton WA
Yep for services over 300 volts phase to phase its switch-fuse-meter. The utility will often lock the disconnect with there lock. I typically use a non-fused disconnect.

The first commerical job I did 20 some years ago the utility had just adopted that meter disconenct standard, I read it and didn't really get it. Can't be a disconnect ahead of the meter...
So my installation was turned down and I had to install a disconnect ahead of the meter.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals