Per 210-21(b), would you consider a duplex outlet a single receptacle?
Can a 15 Amp duplex be installed on a 20 Amp circuit without any other outlets?
(I've got somebody that won't believe me)
Top
2017 / 2014 NEC & Related Books and Study Guides
#79852 - 01/31/02 05:10 PM Re: Single Recp.
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
The FPN refers us to article 100. (Definition of receptacle)

“A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.”

A duplex is a multiple outlet device by definition.

Yes on 15A duplex receptacle can be protected by a 20A breaker.
Top
#79853 - 02/04/02 05:19 PM Re: Single Recp.
daniel damon Offline
Member
Registered: 01/02/02
Posts: 31
Loc: Ambler,PA, USA
Nick,

I am not sure but if it is a dedicated 20 amp line, you must use a 20amp recp.I could be wrong.
Top
#79854 - 02/04/02 05:31 PM Re: Single Recp.
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Only if it's a 'single' receptacle. A duplex is not a single receptacle by definition.
Top
#79855 - 02/04/02 06:06 PM Re: Single Recp.
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Ditto Nick. A duplex is 2 receptacles and, therefore a 15 amp is acceptable, even on a dedicated line.
Top
#79856 - 02/06/02 05:03 AM Re: Single Recp.
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Thanks, fellers. Although I originally showed the "stuporintendent" the exact same chain that Nick mentioned, he wouldn't agree. I asked you, printed this thread, and brought it in to him. He's now shut up but he's mad :
Top
#79857 - 04/17/02 05:47 PM Re: Single Recp.
Dude123084 Offline
Junior Member
Registered: 04/16/02
Posts: 10
Loc: Mc Keesport, PA, USA
If you take a duplex, break off the hot and neutral tabs, and feed two circuits into it, would it be considered 2 single outlet circuits?
Top
#79858 - 04/17/02 06:47 PM Re: Single Recp.
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
It still would not meet the definition of a single receptacle because it is still two devices on one yoke.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals