The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79798 - 01/25/02 04:18 PM GEC through Primary Conduit
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Is it allowable to bring the secondary GEC for a separately derived system (aka xfrmr) through the conduit with the primary feeder and terminate it at the service GEC?
(No problem with capacity, service GEC/Ufer is a 3/0)

Top
2014 / 2011 NEC & Related Books and Study Guides
#79799 - 01/25/02 05:36 PM Re: GEC through Primary Conduit
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Electure, 1999 code 250-30, and all others for the 30 years I've been around, the grounding electrode must be as near as practicable to the transformer. If there is NO way to bond it closer I can't off the top of my head find fault (no pun intended) with your method. If there is a way, you would be in violation not to use it, including a ground rod, etc.. I'd have to consider the capacitance of the method, I really don't like, at first blush, it being mixed in with phase conductors of the primary side, too danged much choke for fault purposes for my liking.

Top
#79800 - 01/25/02 05:41 PM Re: GEC through Primary Conduit
johngeorge Offline
Member

Registered: 09/08/01
Posts: 32
Depends on the type transformer and system you are referring to. You can ground the secondary of the transformer at the transformer and run an equipment ground with the conductors feeding the panel or use the neutral (if this is a grounded system) as ground to the panel and ground the panel as you would a service. Using the neutral generated at the transformer as the ground to the panel, is much more practicle.

Top
#79801 - 01/25/02 06:29 PM Re: GEC through Primary Conduit
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Sorry (again) for a bad explanation.
45 KVA 480X120/240 Delta. It's about 6' from the service. Seems almost silly to run a separate conduit??

Top
#79802 - 01/25/02 06:49 PM Re: GEC through Primary Conduit
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Scott,
I posed this question a couple of weeks ago to the chief electrical inspector for the City of Los Angeles in a grounding class he taught at our shop.

He had a drawing of a typical panel (480/277) feeding a transformer feeding a panel. (120/208). I asked if the 480/277V panel in the diagram was the service equipment, would it be acceptable to run the grounding electrode conductor through the primary conduit with the primary feed to the building grounding electrode system.
Answer: Yes
However, now the primary conduit must meet the same bonding requirements as a GEC in it’s own metal conduit.

You could accomplish that pretty cheap by punching your KO’s and using bonding lock nuts.

PS: I got the colored MC from Alflex. Now I have every color combonation under the sun. What an invintory nightmare! It will make for a nice instal when we are done though.


[This message has been edited by Nick (edited 01-25-2002).]

Top
#79803 - 01/26/02 07:20 AM Re: GEC through Primary Conduit
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
PS again: That would also mean no flex connection on the primary.

Top
#79804 - 01/26/02 08:12 AM Re: GEC through Primary Conduit
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
I think it is poor practice, but not a violation if installed per 1999 NEC 250-64(e).

Remember, that the bonding bushing (on any type of KO, one hole or concentric ) must be connected to the GEC and not just the enlosurer(s) (boxes).

Top
#79805 - 01/26/02 06:01 PM Re: GEC through Primary Conduit
Elzappr Offline
Member

Registered: 12/20/01
Posts: 273
Loc: Oregon
If the specs allow you to NOT install flex between the panels and the transformer, and if the transformer is not to big and noisy, then I think that would be a really cool way to go, with bond bushings at each end of the conduit nipples, and lay-in lugs in the transformer case for the GEC. Remember, the code allows you to connect your derived panel's GEC right to the ground bus of the service panel [250(a)(3)(c)exc.].

Top
#79806 - 02/03/02 07:55 PM Re: GEC through Primary Conduit
Tom Baker Offline
Member

Registered: 10/09/01
Posts: 31
Loc: Bremerton WA
I install a lot of 200 amp 480 volt service for pump stations, with a 5 kva lighting transformer. These do not have structural steel so the nearest avavilable electrode is the building GE system. I'll run from the lighting panel through the raceway and then outside to the ground rods. Ii its a metal enclosure or raceway I bond at both ends, this makes a lot of work and is a good time and materials job.

If possible I'll run straigt outside and use PVC conduit to sleeve it. Sometimes I'll go out through the service disconenct (primary, if you will).

For connections to the lighting transformer, Ilve started using liquid tight non-metallic flex. Then I don't have to bond the flex.