The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 97 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79773 - 01/24/02 07:03 AM 99, 300-3b?SE 3wire?
Cindy Offline
Member

Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
(b) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, CABLE, or cord, unless otherwise permitted in accordance with (1) through (4). [not applicable here]

i've understood this to mean that you can't run SE cable with 2 ugc's and 1 gc from a service disconnect panel to a sub-panel, and then run a separate 4awg cu egc [you know, outside the sheath].
i saw this in a new house and it made me question what i thought i knew. -C-

Top
2014 / 2011 NEC & Related Books and Study Guides
#79774 - 01/24/02 02:51 PM Re: 99, 300-3b?SE 3wire?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Some folks are just creative & believe that if it works, it must be safe.

You are reading the section correctly, they should have run SER cable, which containsd a bare equipment ground.
_________________________
Few things are harder to put up with than the annoyance of a good example.