The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
10/21/16 09:09 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 132 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79769 - 01/22/02 10:04 AM bonding
ggardiner Offline

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
Does any one know of a requirement on the number of threads a bolt should have when bolting down a attachment for bonding. According to URL if the size of conductor is a #6 wire then it should be secured by a 1/4 bolt, it does not state what is considered enough threads to have a secure hold. I have heard a minuim of three complete threads but I can't find anything to back this up with the way it is written it looks like you could get away with a half of thread as long as it looked secure.
Anyone one got any ideas?

2014 / 2011 NEC & Related Books and Study Guides
#79770 - 01/22/02 03:17 PM Re: bonding
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
With the thickness of a 4-S box (.0625"), and pitch of a 10-32 ground screw (.03125"), you get less than 2 threads fully engaged.
With a box >100sq" (.053") and a 1/4-28 NFT screw's pitch (.0357") you get less than a turn and a half of screw engaged.

#79771 - 02/11/02 11:51 AM Re: bonding
bob3232 Offline
Junior Member

Registered: 02/10/02
Posts: 4
I would think you would have to use all the threads that the nut consumes.anything past the nut does nothing.Every thread not used under the nut would be weaker at every 360 degrees.Just my opinion.

#79772 - 03/06/02 07:59 AM Re: bonding
DB Offline

Registered: 03/05/02
Posts: 18
Loc: St. Louis
For bonding large wires (above 12GA) in junction boxes use a servit post. A servit post is like a split bolt connector (a servit) but it has a stud on the end that is used to bolt it to the box.

This make a very solid connection. Burdy (FCI) makes a fine product.