The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (sparkyinak, LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79769 - 01/22/02 10:04 AM bonding
ggardiner Offline
Member

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
Does any one know of a requirement on the number of threads a bolt should have when bolting down a attachment for bonding. According to URL if the size of conductor is a #6 wire then it should be secured by a 1/4 bolt, it does not state what is considered enough threads to have a secure hold. I have heard a minuim of three complete threads but I can't find anything to back this up with the way it is written it looks like you could get away with a half of thread as long as it looked secure.
Anyone one got any ideas?

Top
2014 / 2011 NEC & Related Books and Study Guides
#79770 - 01/22/02 03:17 PM Re: bonding
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Interesting!
With the thickness of a 4-S box (.0625"), and pitch of a 10-32 ground screw (.03125"), you get less than 2 threads fully engaged.
With a box >100sq" (.053") and a 1/4-28 NFT screw's pitch (.0357") you get less than a turn and a half of screw engaged.

Top
#79771 - 02/11/02 11:51 AM Re: bonding
bob3232 Offline
Junior Member

Registered: 02/10/02
Posts: 4
I would think you would have to use all the threads that the nut consumes.anything past the nut does nothing.Every thread not used under the nut would be weaker at every 360 degrees.Just my opinion.

Top
#79772 - 03/06/02 07:59 AM Re: bonding
DB Offline
Member

Registered: 03/05/02
Posts: 18
Loc: St. Louis
For bonding large wires (above 12GA) in junction boxes use a servit post. A servit post is like a split bolt connector (a servit) but it has a stud on the end that is used to bolt it to the box.

This make a very solid connection. Burdy (FCI) makes a fine product.