#79752 - 01/17/02 08:39 AM Coal Mine/ MSHA
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
i am looking at doing three buildings at three different coal mines. the building will b some kingd of lab. just lights and recepts.

i am trying to decide whether to use EMT, ENT, BX, or MC for these buildings..

the area is not classified.

anything else i should consider?

-regards

frodo
Top
2017 / 2014 NEC & Related Books and Study Guides
#79753 - 01/17/02 02:06 PM Re: Coal Mine/ MSHA
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
You can forget the BX unless you get the kind with an equipment grounding conductor in it, the Fed's will require this.

I usually use MC for concealed work & EMT (with an equipment ground pulled in) for exposed work.

I'd say forget the ENT, knowing how mine inspectors think, they probably wouldn't care to see it.

For circuits up to #6 AWG, your equipment ground must be sized 100% of the hot conductor, #4 & up it must be at least 50% of the hot conductor. This could be a problem if you tried to run any cable larger than #10, since the equipment ground will be too small.

What state will this be in?

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#79754 - 01/17/02 06:19 PM Re: Coal Mine/ MSHA
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
hi,
thanks for the reply. two of the labs is in southern indiana and the other is in kentucky.

in a drop in cieling then just using flex would be adequate for the light fixtures, and run emt everywhere else?

ent would probably scare even those mine guys!

-regards

frodo
Top
#79755 - 01/18/02 05:52 PM Re: Coal Mine/ MSHA
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Yeah, they understand flex. The biggest thing, as I pointed out, is to have an equipment ground in every raceway.

I'll be doing a Bath House & motor Barn in Mossy, WV, probably next month. The Bath House is portable, being built about 6 miles from where I live & we'll ship it on flatbeds. The motor barn will be built on site.

I've been to Inez, Kentucky a few times, thats about as far from Indianna as you can get & still be in Kentucky.

Toim

[This message has been edited by Tom (edited 01-18-2002).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals