The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 221 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#79709 - 01/13/02 02:04 PM Appliance cords
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Can anyone tell me where to find code info on sizing appliance cords? I can not seem to find anything regarding dishwashers in particular. Seems most electrical appliances come with cords rated for less than a 15 or 20 amp circuit. I would like a definitive answer on installing a cord on a dishwasher. Thanks....Scott

Top
2014 / 2011 NEC & Related Books and Study Guides
#79710 - 01/13/02 07:34 PM Re: Appliance cords
Elzappr Offline
Member

Registered: 12/20/01
Posts: 273
Loc: Oregon
Some of the info can be found in 422-16(b)(2). Length 3' to 4' from grounding type plug on cord to rear of appliance.
Then check out 240-4 for wire size and OC protection relative to what the nameplate of your dishwasher says. Probably SP type cord (table 400-4) 14 or 12 AWG. You really need to check out the local code because this is a subject frequently visited and amended by state and local authorities.

Top
#79711 - 01/14/02 01:57 PM Re: Appliance cords
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
In general, ampacities of most common types of flexible cord can be found in Table 400-5(A) You can usually use Column B, but check out the small print at the bottom of the table.

Here's an example, 2 burner hot plate draws 20 amps, needs to be on a 30 amp breaker since it will be on all day. Branch circuit conductors are #10, but the cord only needs to be a maximum of #12.
_________________________
Few things are harder to put up with than the annoyance of a good example.